Jason,

The M190 requires using a 15-amp (maximum) branch circuit. As long as the total current from both types of inverters doesn't exceed 12 amps (80% of 15), there should not be a problem in mixing the inverters. The combination you are proposing is only 8.6 amps -- it should be fine.

Kent Osterberg
Blue Mountain Solar, Inc.
www.bluemountainsolar.com

On 5/18/2013 3:26 PM, Jason Szumlanski wrote:
Is there any reason I can't do this? I have an existing string of 3 M190's and want to add 7 M215's. I plan to tie into the same j-box, which has #10 going to a fusible disconnect and a supply side tap. I'll just have to change the fuse rating.

Any comm issues reported with this setup?

Jason Szumlanski
Fafco Solar


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to