Dick,
No, I stand by what I wrote, but I'll clarify. If the gennie has a GFI, it will often have trouble feeding an inverter, as the GFI will sense the ground loop and trip. The ground loop is caused by bonds in both gennie and the first point of AC disconnect on the inverter's output (a.k.a. the AC bond point in the E-Panel or equivalent). You won't ever want to remove the neutral-ground bond in the E-Panel, as then you'd only have a bond when plugged into the gennie. This is why inverters designed for RV's are listed to UL 458 rather than 1741 - they have an internal relay to make/break the neutral/ground bond. When boondocking it's made, but when plugged into shore power it's open, allowing the utility hookup to bond at the meter. I asked Wiles about this years ago, as there's no fully Code-compliant way to deal with this issue, in an off grid system with a contractor's special gennie with an unbreakable bond. He said the least unsafe approach is to leave the ground loop in place and allow the grounding conductor of the gennie cord to carry some of the neutral current (which implicitly means bypassing any GFI). But in this case, the ground loop may in itself be the source of the appliance's failure to run off of the inverter. It's thus worth trying this approach. If it works with the grounding conductor open, then that's the likely cause. The move the gennie far enough from any building with inverted AC, treat it like a "separate structure" per NEC, ground the bonded chassis to its own rod(s), and you've done all you can. If there's a ground fault in the coffee maker, no problemo, as the cofeemaker metal is grounded through the bond in the E-Panel. It's just the gennie that's not bonded to the main system ground. High quality commercial and industrial generators allow the bond to be either bonded or floated, but homeowner units often can't be floated. Therein's the problem(o). Clear as mud? Allan Allan Sindelar Allan, I think most gennies bond the neutral to the chassis so the circuit breakers on the gennie will trip in the event of a ground fault. If the neutrals weren't bonded and the breakers didn't trip to clear it, there would be a shock hazard on the chassis in the event of a fault. Not sure what you mean by suggesting to disconnect the grounding conductor on the extension cord. If there's a ground fault in the coffee maker, that might leave any metal parts of the appliance energized and thus be an extreme shock hazard. Better to investigate the gennie for a ground to neutral bond as well as the inverter BOS and rewire so the is only one neutral to gound bond in the entire system, as required by code. Apologies in advance if I have misunderstood your suggestion. Your posts are invariably right on.Dick Ratico Solarwind Electric Jeremy, Outback may be right on, and it's worth checking. Most portable gennies internally bond neutral to chassis, because they expect that no typical homeowner will ground the chassis. (Inverter-generators are a noteworthy exception to this.) Most inverter systems also have a neutral-ground bond, if done to Code. Whe plugged into the gennie, there's thus an inherent ground loop. Try disconnecting the grounding conductor on the extension cord. Allan Allan Sindelar al...@positiveenergysolar.com NABCEP Certified Photovoltaic Installer NABCEP Certified Technical Sales Professional New Mexico EE98J Journeyman Electrician Founder and Chief Technology Officer Positive Energy, Inc. 3209 Richards Lane (note new address) Santa Fe, New Mexico 87507 505 424-1112 www.positiveenergysolar.com On 6/7/2013 9:10 AM, All Solar, Inc. wrote: I found out that the appliance will work fine from an extension cord with a portable generator. The appliance will not even work however when the backup gen is running and transfering through the inverters. Outback T.S. suggested to check the Neutral to ground bond so that is the next step. Also tried to set the Power Save levels the same (stacked pair) Jeremy All Solar ----- Original Message ----- From: Exeltech To: RE-wrenches Sent: Wednesday, April 17, 2013 1:51 PM Subject: Re: [RE-wrenches] Outback wave form Wrenches, While the addition of a capacitor may resolve issues associated with various inverter/appliance/motor combinations, please make sure the capacitor(s) get switched OUT of the circuit (disconnected) when the load itself is disconnected. Failure to do so could under some circumstances cause the inverter control-loop circuitry to go unstable, leading to unpredictable inverter operation, and possible damage/failure in the power system. Disconnecting the capacitor with the load alleviate this possibility. Regards to all... Dan Lepinski --- On Wed, 4/17/13, Larry Crutcher, Starlight Solar Power Systems <la...@starlightsolar.com> wrote: From: Larry Crutcher, Starlight Solar Power Systems <la...@starlightsolar.com> Subject: Re: [RE-wrenches] Outback wave form To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org> Date: Wednesday, April 17, 2013, 2:09 PM We experience issues like this from time to time. PF seems to be the culprit. Have you measured it or looked at the waveform yet? How an inverter deals with PF seems to vary broadly. For example, the Splendide XC2100 washer/dryer will not work on a Magnum Energy and a few other sine wave inverters. However, it will run on a low cost GoPower or Samlex sine wave inverter. Below is a scope trace of voltage/current of the Magnum inverter & Splendide washer. Upper trace is voltage By adding a 50uF run capacitor inline, it somewhat tames the current phase and the sine wave so the Magnum can operate the washer. (Special thanks to Al for the discovery and photos) Larry Crutcher Starlight Solar Power Systems On Apr 16, 2013, at 9:46 AM, All Solar <allso...@scswifi.net> wrote: Have a client with a new coffee maker that will not run from their new dual outback setup. Has anyone heard of this lately. We have had no problems with appliances and sine wave inverters. What to look for? Sent from Jeremy's IPhone. Sorry for typos and shorthand! _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org -----Inline Attachment Follows----- _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org |
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org