Dear Fellow Wrenches,

We have a small 50kW 120/208V commercial job with five 9kW 3PH inverters, each 
outputting max. 25A.  We are landing those into a dedicated load center with 
five 40A breakers. Doing the math, 5 x 25A x 1.25 = 156.25A, we would need a 
160A breaker.  This also equals to the maximum we can backfeed into a 800A/800A 
Main Service on the load side according to the "120%" rule.

The problem now is that we cannot locate any kind of 160A breaker or even a 
160A fuse for a AC disconnect.

Has anybody ever done this without doing a "line-side tap?" It is hard to 
believe that there wouldn't be an existing solution to landing maximum PV into 
a 800A service. Are we missing something?

Any good ideas or comments would be appreciated.

Sincerely,

Pekka Laine

President
Photon Solar Power Inc.
www.PhotonSolarPower.com
Cell. 760-556-8170
Toll Free 888-SUN-ACDC
CA Lic. #933648
NABCEP Certified PV Installer # 032611-174
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to