Tom,
Except that absorb starts off at 100% of the available amps, not 50%. Absorb starts as soon as bulk reaches the bulk voltage setpoint. It starts out at the same current as was available in bulk, then ramps back incrementally as the batteries continue to approach full, allowing only as much of the available current to flow to the batteries as is necessary to maintain the voltage setpoint plus loads. On the finishing end, absorb doesn't have much to do with available amps. Rather, it either completes a timed cycle, with no particular control of the available amps except as regulated as above, or it switches to float when the amps necessary to maintain the bulk (a.k.a. absorption) voltage drops below a threshold, typically 2% of bank capacity. And finally, the midpoint between 20 and 50 is 35, not 40. Given that these principles form the basis of your definitive .42 figure, this number sounds pretty arbitrary. Is there anything more you can say by way of explanation? Thanks, Allan Allan Sindelar
Jay Sorry I should have explained that too... Absorb starts off at around 50% of the available amps and tapers down to around 20% So I divided 20 by 50 = .40 there's a 5% loss factor hence .42Tom Duffy Senior Solar Design Engineer Toll Free 888-895-8179 t...@thesolar.biz Customer Service and Accounting 888-895-6810 Grid tie sales 888-895-7847 Off Grid sales 888-895-4058 Other Product Sales 888-895-9612 Central America Sales (Panama) 507-6-126-1253 Shipping and Receiving 888-895-6497 Tech Support 888-895-8179 SKYPE: thesolarbiz -----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Jay Peltz Sent: Monday, July 22, 2013 1:27 PM To: RE-wrenches Subject: Re: [RE-wrenches] Trojan L-16s Hi Tom Where did you get the .42 from? Jay Peltz power Sent from my iPhone On Jul 22, 2013, at 11:04 AM, Tom Duffy <t...@thesolar.biz> wrote:Drake Keep the absorb rate recommended for the CC. The trimetric strays over time and will become accurate again when you overcharge (equalize) The math: Amp hours of battery @ 20 hour rate divided by max charge available in amps, from whatever you using to charge (solar or inverter/charger) Times .42 = absorb time in hours i.e. your system 980 watts, 980 divided by 28.8 (average volts) = 34 amps max charge 370 AH divided by 34 = 10.88 X .42 = 4.57 round up to 4.6 hours absorb time for the CC Your inverter VFX3524 max charge 85 amps... 370 divided by 85 = 4.35 X .42 = 1.82 absorb time for the inverter/charger when running generator Tom Duffy Senior Solar Design Engineer Toll Free 888-895-8179 t...@thesolar.biz Customer Service and Accounting 888-895-6810 Grid tie sales 888-895-7847 Off Grid sales 888-895-4058 Other Product Sales 888-895-9612 Central America Sales (Panama) 507-6-126-1253 Shipping and Receiving 888-895-6497 Tech Support 888-895-8179 SKYPE: thesolarbiz -----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Drake Sent: Monday, July 22, 2013 10:04 AM To: RE-wrenches Subject: Re: [RE-wrenches] Trojan L-16s Hi Larry, I will bump up the absorb voltage to 29.6 V. How long do you think the bank should stay in absorb at that rate? The bank now seems healthy, with the bad battery replaced. It does accept charge, without going high prematurely. The max charge rate from the array is around C/10. The system can also be fast charged from a Honda 6500 inverter generator through the Outback 3524 VFX. We have a Trimetric meter on the system. The discrepancy between the percent charge and the voltage is what demonstrated that we had a problem. Thanks, Drake At 09:30 PM 7/19/2013, you wrote:Hi Drake, It always concerns me when I hear that a battery bank reaches absorb setting very quickly. It typically means one of two things: very few AH were removed from the bank; the battery bank has sulfated cells due to chronic undercharging. Far too often I find the latter to be true. Healthy batteries will accept current and hold the charge voltage down with a fairly linear, slow climb to absorption voltage. Sulfated batteries do not accept current well which allows voltage to climb rapidly as the battery presents little load on the charging system. I'm not sure how this plays into your original post about a bad cell but it seemed worth mentioning. My opinion is to aggressively charge, by using higher voltage, large flooded batteries. This is especially true when the PV system is moderate or undersized. 29.6 volts is what Trojan recommends. You can go as high as 32 volts on the L-16's but make sure the temperature compensation is installed properly and working. You will use more water. One last comment, I highly recommend that ALL off grid systems have a battery capacity monitor installed. It's kind of like flying an airplane without a fuel gauge...it might not end in disaster. Larry Crutcher Starlight Solar Power Systems On Jul 18, 2013, at 1:11 PM, Drake <drake.chamber...@redwoodalliance.org> wrote: Tom, The batteries usually reach absorb voltage shortly after the sun hits the array. The reason the bank wasn't working correctly is that one cell was dead in one of the batteries. I could increase the absorb time to 4.6 hours and the voltage to 29.6, especially since the bank has a new battery. That is longer and higher than I'd previously heard recommended. What would be the effect on water consumption? How did you calculate the absorb time? Thanks, Drake _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org |
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Change email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org