HI Rich,

Grainger will have 12v coil relays that will switch 48v.


jay

peltz power
On Aug 8, 2013, at 4:49 PM, Rich Nicol wrote:

> Hello Wrenches,
>  
> Does anyone have any advice about what to use for a relay to power a 48 volt 
> Zephyr battery vent fan using the 12 volt auxiliary output from the Midnite 
> Classic Charge controllers. The fan only draws 6 watts but my problem is the 
> 48 volt side of the equation. A supplier has recommend  a double pole/double 
> throw relay rated for up to 30 amps at 24 volts wired in series. I’m curious 
> if anyone knows of a relay rated for 48volts (actually higher voltage since 
> the fan is signaled to come on when the battery reaches gassing voltage) that 
> would work in this application or if there is widespread agreement that the 
> 24volt rated relay would work fine since we are requiring only minimal 
> current and spreading between two contacts.
> As always, your input is greatly valued!
> Thanks,
> Rich
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to