Jay,

You surmize correctly on both points.  12.0V equates to ~50% DOD.  The LVD 
point should be higher.  The actual value depends somewhat on the battery type 
and ambient temperature, but under lightly loaded conditions (e.g. C/30), the 
LVD should be adjusted for around 12.4Vdc to keep the discharge to 20% or less.

Dan

--------------------------------------------
On Thu, 1/2/14, jay peltz <j...@asis.com> wrote:

 Subject: Re: [RE-wrenches] Higher LVR to force full re-charge in small OGPV 
systems
 To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
 Date: Thursday, January 2, 2014, 7:37 PM
 
Hi All,

I've been wondering about the LVD set point for this project and I'm asking 
what you all think.
So far 12.0v has been chosen for the LVD and 13.8 LVR.

But IMHO as the PV might do 15-20% at best avg per day, I got to thinking that 
at 12v, its around 40-50% SOC, so it might be the system could be off for a few 
days as it recharges.

If the LVD was higher then it would bounce around at at higher SOC  with a 
lesser chance of off for days and hopefully at least some lights every day.

curious what you think,

thanks,

jay