All,

I think that in the past, list discussions have talked about fusing of parallel battery circuits as a best practice, but it's required per 690.9 right? (text below from 2008 NEC)

Also, if someone (don't look at me) really wants to use 2 parallel circuits of 12V batteries, what equipment is recommended to provide overcurrent protection? The installer is using Outback hardware (FW500?) and has two battery circuits combined in the battery enclosure and run to a Big Bus feeding the two 125A dc disconnects for two GVFX3648s. If you've read this far, this area is more your wheelhouse than mine. Thanks in advance!


690.9 Overcurrent Protection
(A) Circuits and Equipment. Photovoltaic source circuit, photovoltaic output circuit, inverter output circuit, and storage battery circuit conductors and equipment shall be protected in accordance with the requirements of Article 240. Circuits connected to more than one electrical source shall have overcurrent devices located so as to provide overcurrent protection from all sources.

Exception: An overcurrent device shall not be required for circuit conductors sized in accordance with 690.8(B) and located where one of the following apply: (a) There are no external sources such as parallel-connected source circuits, batteries, or backfeed from inverters. (b) The short-circuit currents from all sources do not exceed the ampacity of the conductors.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to