Hi David,

Can you elaborate on the mounting system(s?) that would minimize fire propagation?

TIA,

Bill Loesch
Solar 1 - Saint Louis Solar
314 631 1094

On 06-Feb-14 1:11 PM, David Brearley wrote:
William,

There are few Class A fire-rated PV modules on the market today:

http://www.trinasolar.com/us/product/PDG5.html

http://www.silicon-energy.com/products/modules

The broader context is that UL is in the process of revising the way that fire ratings are determined for PV systems. To date, modules have received a fire classification. However in the installed environment, fire propagation has more to do with the mounting system than with module construction. Therefore, fire classification tests in the future will be based more on the mounting method.

As Bill Brooks explained here on January 8th:

UL 1703 has been substantially changed as to how modules are fire rated. 
Basically, modules will no longer receive a direct fire rating unless they are 
installed in a fire-rated mounting system. A current module with a Class C or 
Class A rating will no longer have that rating. The mounting system will carry 
the fire rating. Modules will have specific “types” based on their 
construction. This way a rack manufacturer can get a fire rating on modules of 
a particular module construction type and not have to rerate their rack with 
every module that has that same construction.

All these changes in the UL1703 standard are going to require education so that 
fire officials and building code enforcement officials understand how to 
enforce the new building code rules in light of the new version of the UL 
standard.

Arguably, enforcement of fire rating requirements in the I-codes is running ahead of the development of the applicable UL standard. It's safe to say that working groups at SEIA and SolarABCs are very interested in tracking these types of issues. The SolarABCs has had fire classification ratings on its radar for several years now:

http://www.solarabcs.org/current-issues/fire_class_rating.html

David Brearley
Senior Technical Editor,/SolarPro/magazine
NABCEP Certified PV Installation Professional
[email protected] <mailto:[email protected]>
Direct: 541.261.6545





On Feb 6, 2014, at 12:20 PM, [email protected] <mailto:[email protected]> wrote:

*From:*William Korthof <[email protected] <mailto:[email protected]>>
*Subject:**[RE-wrenches] Solar Module fire ratings*
*Date:*February 6, 2014 10:56:05 AM CST
*To:*[email protected] <mailto:[email protected]> *Reply-To:*RE-wrenches <[email protected] <mailto:[email protected]>>


I've just been informed by a city (our own City in fact) that is asking for minimum Class-B fire-rated solar modules, citing rules newly adopted Jan 1, 2014. The expert behind the counter made reference to IRC section 902.4, which seems to call for solar installations to meet the same fire rating standard as the roofing on which they are installed. It was the end of the day. Most roofing is B or A rating apparently, and my official was adamant that this meant only a B or A rated panel would be allowed.

As far as I know, virtually every solar panel I've ever handled going back to the mid 90's was Class C rated. The only Class A I remember (and the only one I noticed from web searching) was the obnoxiously unwieldy glass-on-glass 300-watt series that got absorbed by Schott and probably discontinued many years ago. I have one of those antiques in my shop for fun, and I encountered exactly one installation that used the product (from another installer), and there were "issues" with the panels within the first 10 years.

Is this Class A/B requirement issue true? Did the state fire marshall adopt a policy at the start of this year that basically bans all panels with C rating?
Are there any class B or A rated modules on the market?
Who's brilliant idea was this?

/wk
--
William Korthof <http://www.sustainsp.com/images/SSP_Logo_RGB_email.jpg>
714.875.3576 and 800.524.2970
Sustainable Solutions Partners
(also dba: EE Solar)





_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



No virus found in this message.
Checked by AVG - www.avg.com <http://www.avg.com>
Version: 2014.0.4259 / Virus Database: 3684/7068 - Release Date: 02/06/14





-----
No virus found in this message.
Checked by AVG - www.avg.com
Version: 2014.0.4259 / Virus Database: 3697/7071 - Release Date: 02/07/14
_______________________________________________
List sponsored by Home Power magazine

List Address: [email protected]

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to