Thanks for your suggestions. I wanted to get ideas before heading out the site 
since it is 4 hours away and in the middle of nowhere with no local resources!

I'll followup once I go visit.


thanks,

Troy Harvey
---------------------
Principal Engineer
Heliocentric
801-453-9434
tahar...@heliocentric.org



On Feb 12, 2014, at 11:43 AM, Ray Walters <r...@solarray.com> wrote:

> I just had an idea on this situation from August's comment.  I'm sure you've 
> checked already, but are you sure that ground and neutral aren't bonded in 
> both locations, causing current to flow through the ground system? I've seen 
> many multiple building properties inadvertently send both a ground wire and 
> neutral to a separate structure with neutral bonded to ground in both 
> locations.
> If the separate structure has its own grounding system and bond, then 
> disconnect the ground wire connection back to the other building, as it will 
> still be bonded through the neutral.  The other option is to set a separate 
> ground buss in the load center at the separate structure, and unbond neutral 
> from ground, since it would bonded back at the other building.
> Just an idea,  I've seen all sorts of weird things happen with current flow 
> on the ground.  If you have uneven current flow on that long a run, it could 
> definitely cause some issues.
> 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> 
> On 2/12/2014 9:14 AM, Exeltech wrote:
>> Troy,
>>  Elsewhere in this thread, boB (Midnite) suggested connecting one of the 
>> problematic lights and dimmers directly at the inverter output.
>>  This is a very sound recommendation, and would immediately rule in .. or 
>> rule out the conductors (and related circuits) as an issue.
>>  Another Wrench suggested using an oscilloscope to check the waveform at the 
>> load end.  This too is excellent advice, and would be even more telling than 
>> connecting the lamps and dimmer directly at the inverter.  The ‘scope will 
>> reveal the AC voltage AND a visual indication of any waveform distortion, 
>> either aspect of which could potentially cause the flicker you describe.
>>  If you don’t have access to a ‘scope, boB’s comment about connecting at the 
>> inverter won’t require any test equipment.
>>  At a minimum, set your DVM to record the voltage minimum; connect it the 
>> lamp circuit, and turn on the 1 kW load you described.  If the voltage is 
>> dropping notably, this too would introduce visible flicker.  The DVM method 
>> is less accurate than an oscilloscope, but better than nothing, and depends 
>> greatly on the quality (or not) of your DVM.
>>  The above aside, anything else would be strictly conjecture .. which we can 
>> do all day, and never be correct.
>>    Dan
>>      --------------------------------------------
>> On Wed, 2/12/14, August Goers <aug...@luminalt.com> wrote:
>> 
>>  Subject: Re: [RE-wrenches] Long transmission line inductance and LED light 
>> flicker
>>  To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org>
>>  Date: Wednesday, February 12, 2014, 9:01 AM
>>    Hi Troy,
>> 
>> Have you double checked that your grounding systems both in the house and at 
>> the inverters/array are all up to snuff?
>> 
>> Sorry I can’t offer any help with the inductance issue.
>> 
>> Best,
>> 
>> August
>> 
>>  
>> From: re-wrenches-boun...@lists.re-wrenches.org 
>> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Troy Harvey
>> Sent: Tuesday, February 11, 2014 5:45 PM
>> To: RE-wrenches
>> Subject: Re: [RE-wrenches] Long transmission line inductance and LED light 
>> flicker
>> 
>> 
>> Richard,
>> 
>> 
>> The system configuration is:
>> Approx 24.7kW of modules connected to:
>>             2 x 9kW Sunnyboys
>>             1 x 5kW Sunnyboys
>> 
>> Plus
>> 4 x 6kW sunnyislands, with 2 Parallel 48V Strings of (12 x 4V Surrettes ) 
>> using 350MCM cable
>> 
>> 
>> 
>> Wire
>> 
>> The wire is about 1000 feet long 350 MCM in a "twisted" bundle to this 
>> outbuilding
>> 
>> Conditions
>> 
>> The conditions were during the day with full sun, so during the test there 
>> is approx. 47kW of available inverter pointed at only >15 amps (120V) of 
>> load(!).
>> 
>> The steady state conditions was a few LED lights, maybe 60 watts worth, plus 
>> a handful of vampire loads, maybe 100-200 watts total. When a pure 
>> resistance load, like a 1000W curling iron was turned on the lights would 
>> flicker.
>>  Since the lights flickered from a resistive load, but didn't stay dim, I 
>> assumed it was from a reactive-phase issues due to the transient  turn-on - 
>> screwing with the LED dimmer circuits which are already doing a bit of magic 
>> to turn TRIAC waveforms into a DC constant current.
>> 
>> thanks,
>> 
>> Troy Harvey
>> ---------------------
>> Principal Engineer
>> Heliocentric
>> 801-453-9434
>> tahar...@heliocentric.org
>> 
>> 
>> 
>> _______________________________________________
>> List sponsored by Home Power magazine
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out participant bios:
>> www.members.re-wrenches.org
>> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to