Dan,
690.10(C) doesn't say no. It says that if you have a single 120V
inverter output connected directly for a 120/240 panel then you can't
put a 240V load in the panel-- in this case you'd either have L
connected to both phases of the panel or I guess you could just use half
the breakers in the panel. For a 240V load it would just see 0 volts
phase to phase, but for a multi-wire branch circuit with current on both
legs you'd potentially overload your neutral conductor.
Now when you use either a 240V inverter (or two stacked 120s) or an
autotransformer between the inverter and the panel, 240V loads are fine
since you have two lines 180 degrees out of phase and voila, 240V.
690.10(C) wouldn't apply to this situation since your inverter(s) would
be supplying 240V (not 120) to your 1P 3W panel.
DKC
On 2014/3/19, 20:40, Dan Fink wrote:
Esteemed Wrenches;
Can anyone here help me with some simple talking points for clients
installing off grid systems? 240 Well pumps hard wired to panel
breakers are common, but everybody (who has even a chance of surviving
up here in middle of nowhere way off grid) NEEDS a 240v welder outlet
in the garage/workshop. But 690.10(C) says no.
Am I missing something obvious? What do I tell these potential clients?
Dan Fink,
Executive Director;
Otherpower
Buckville Energy Consulting
Buckville Publications LLC
NABCEP / IREC accredited Continuing Education Providers
970.672.4342
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org