August,

We're seeing multiple inverters with the same error, and not getting the best 
of answers or support from SMA on fixing the problem so far.  And this is not a 
metal roof; it's PanelClaw on EPDM.

Jeff Irish
Hudson Solar
________________________________
From: re-wrenches-boun...@lists.re-wrenches.org 
[re-wrenches-boun...@lists.re-wrenches.org] on behalf of August Goers 
[aug...@luminalt.com]
Sent: Tuesday, March 25, 2014 8:41 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof

Hi Marco,

Did you ever make any progress on this issue? We’re having an interesting issue 
with one of the new Sunny Tri-Power inverters (a 24 kW unit in this case) where 
we get an error “residual current too high.” We’ve only done a little 
troubleshooting so far but I don’t think we have a ground fault.

Best,

August

Luminalt

From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 
[mailto:re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>]
 On Behalf Of Marco Mangelsdorf
Sent: Friday, March 14, 2014 9:56 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof

Probably not.

From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of RE Ellison
Sent: Friday, March 14, 2014 1:24 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof

Is the metal roof grounded? Just a fast thought.

bob

From: 
re-wrenches-boun...@lists.re-wrenches.org<mailto:re-wrenches-boun...@lists.re-wrenches.org>
 [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Marco 
Mangelsdorf
Sent: Thursday, March 13, 2014 10:31 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Unusual problem with SMA TL inverter on metal roof

Friends,

We have run across an odd technical problem at our commercial install at a 
laundromat on our island.   Attached is the description of the issue from SMA.  
We don’t know much except that we are switch out the TL inverters to the old 
style US inverters because SMA has no fix for the phantom ground tripping.  The 
issue is beyond our feeble understanding.

Any observations to share?

Thanks,

marco

________________________________
No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 2014.0.4336 / Virus Database: 3722/7186 - Release Date: 03/12/14
________________________________
No virus found in this message.
Checked by AVG - www.avg.com<http://www.avg.com>
Version: 2014.0.4336 / Virus Database: 3722/7186 - Release Date: 03/12/14
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to