I recently took a code update course with the electrical inspector in Andover 
MA, and he said that he is only allowing micro-inverter systems in his 
jurisdiction at the moment. 

SolarEdge and other auxiliary optimizers are not able to certify that they will 
shut down within 10 seconds. I understand that the manufacturers are working on 
this, but I'm not sure about their timeframe. Most jurisdictions in MA, I 
believe, are accepting SolarEdge or Tigo systems, but they don't comply at the 
moment with the 10 second shut-down provision in 690.12 (2).

The inspector said that he is interpreting 690.12 (1) to say that the means of 
performing the shutdown should be within 10'/5' of the array, so that means 
locating the shutdown means on the roof in most cases. The last time I brought 
this up on the Wrenches list, it was suggested installers could use some kind 
of relay setup with an accessible activation switch and a relay disconnect. 
However, 690.12 (5) says: "Equipment that performs the rapid shutdown shall be 
listed and identified". 690.12 (5) unfortunately doesn't tell us what the 
equipment should be listed and identified for. It could be listed and 
identified for the circuit characteristics and shutdown time, or it could be 
listed and identified for the requirements of 690.12 as a whole function with 
its own UL specifications. It's possible to find equipment for the former 
interpretation, but I'm not aware of anything available for the latter (is 
anyone writing a UL regime for this?). And I think
 that the latter interpretation is reasonable, given the ambiguity in the way 
the text is written, and what is usually meant by "listed and identified" taken 
together.

I like micro-inverters for small systems. And I like the SolarEdge model for 
larger systems with weird layouts, shading issues, or a premium on production. 
However, central inverters are, depending on the configuration and size of the 
system, 0.05 $/W to 0.25 $/W less expensive than micro-inverters or DC 
optimizer systems, and that increase in cost is most likely to come out of the 
contractor's pocket. I also see this affecting sales for companies producing 
central inverters as the 2014 code rolls out across the country. If someone has 
a solution for central inverters under 690.12 when dealing with skeptical AHJs, 
I'd appreciate hearing more about it.

Regards,
Jeffrey Quackenbush


On Tuesday, May 20, 2014 2:07 PM, Phil Forest <pfor...@southmountain.com> wrote:
 

>
>
>All in all, not longer, glad to say. 
>Strings can have more modules, so there's fewer home runs. Optimizer wires are 
>longer than module wires, they even reach when installing modules in 
>landscape, so fewer jumpers. Be thoughtful when mounting optimizers to rails 
>so it's easy to connect after module is clamped down. Bolts that attach 
>optimizers slide into rails from the end (UniRac SM type rails). You supply 
>your own nuts and bolts. They supply a star washer for bonding optimizer to 
>rail for EG. 
>We mounted optimizers to modules on one job when using UniRac Sunframe. 
>SunFrame is a pain in my neck, optimizers or not. 
>
>Phil Forest
>South Mountain Company
>
>On May 20, 2014, at 1:33 PM, Will White <william.wh...@rgsenergy.com> wrote:
>
>
>Phil,
> 
>Do you find that the DC optimizer adds to the amount of time on an install?
> 
>Thanks,
>Will
> 
>From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
>Of Phil Forest
>Sent: Tuesday, May 20, 2014 1:26 PM
>To: RE-wrenches
>Subject: Re: [RE-wrenches] 2014 NEC
> 
>Will,
>No problems with inspectors for us in MA, regarding rapid shutdown, since we 
>recently switched to using SolarEdge central inverters with optimizer under 
>each module, for roof mounted installs. 
>So far so good. They seem well made and engineered. Tip: you have to enable 
>the arc fault protection when commissioning, ships disabled. 
>Phil Forest
>South Mountain Company
>
>On May 20, 2014, at 10:59 AM, Will White <william.wh...@rgsenergy.com> wrote:
>Wrenches,
>> 
>>Is anyone else having problems with inspectors and the 2014 NEC?  In Mass 
>>we’re having all kinds of issues with inspectors requiring/allowing an array 
>>of different things for 690.12 rapid shut down ranging from roof top 
>>disconnects, disconnects on the side of a house 20’ up, disconnects in 
>>attics, or only disconnects that can be activated on the ground.  It varies 
>>between inspectors.
>> 
>>We’re also having problems with one inspector requiring arc fault breakers on 
>>Enphase even though there are no UL listed arc fault breakers that can be 
>>back fed or he wants us to run the trunk cable in a raceway.  
>> 
>>It’s getting very difficult to install in Mass.
>> 
>>Thanks,
>>Will
>> 
>>Will White
>>Operations Manager - New England 
>>RGS Energy  
>>64 Main St. |Montpelier, VT 05602
>>tel 802.223.7804 |mobile 802.234.3167 |fax 802.223.8980 
>>RGSEnergy.com | william.wh...@rgsenergy.com   
>> 
>> 
>> 
>> 
>> 
>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches@lists.re-wrenches.org
>>
>>Change email address & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address: RE-wrenches@lists.re-wrenches.org
>>
>>Change email address & settings:
>>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>>
>>
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches@lists.re-wrenches.org
>
>Change email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>
>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Change email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to