August:

Thank you for the suggestion.  We started with some Polaris connectors but
they were just too big.  Same may be true with the piercing splices but
worth considering.

I was worrying about the legality of the power flow as well.  I posed the
question in a separate post.

William


Lic 773985
millersolar.com
805-438-5600


-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On
Behalf Of August Goers
Sent: Wednesday, June 25, 2014 11:37 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Split bolt

Hi William,

You might try an insulation piercing connector for this application:

https://www.platt.com/platt-electric-supply/Splicer-Reducers-Insulation-Pi
ercing/Ilsco/IPC-4-0-2-0/product.aspx?zpid=708303

Also, not to get nit-picky, but you might be in violation of the 120% rule
if that is a load side tap.

Just a couple of thoughts.