Friends:
I found the problem: There was a damaged wire immersed in water in the conduit. The voltage was fluctuating at the inverter end and solid at the module end. After testing the Isc a few times the conductor burned through and I was able to pull one end out of the conduit. So, the inverter was doing its job. We still have some wire nut splices which are working fine. I will eliminate them once I replace all of the wire, which is warranted since this is the second conductor failure. The conductors are all TWHN-2 which are wet rated. I need to upgrade to a better conductor. I have never had this type of failure at any other location. I suspect I should consider USE-2. I'd appreciate comments on this subject. My thanks to Steve Jefferson for personal attention to this problem and to everyone who responded. And lastly, I still wonder about the concept of "internally arcing" wire nuts. I wonder if there is any scientific basis for the claim. I will not be using them in PV circuits on general principles. If I do need to splice I will probably use a gangable tubular terminal block. There are more parts to this connector than a wire nut so maybe those might arc. We will see. William Miller Gradient Cap_mini Lic 773985 millersolar.com <http://www.millersolar.com/> 805-438-5600
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org