Thanks to Nick for catching a misstatement in my email, corrected below in *bold*. I was trying to make a general statement out of his specific situation.

On 2014/6/26, 10:20, Dave Click wrote:
NEC says 10' from the array, defined as "A mechanically integrated assembly of modules or panels with a support structure and foundation, tracker, and other components, as required, to form a direct-current power-producing unit. 70HB14_CH00_FM_pi_xii.pdf " I take this to mean that the "array" definition includes support structure, so you could go 10' from the bottom of the pole?

But that doesn't matter, as rapid shutdown requirements only apply to PV systems *[conductors]* "on or in" buildings; it only applies to a ground-mounted system if you bring the dc all the way into *or onto***a building (*if you are >10' from the array or >5' within the structure*). So, Rapid Shutdown doesn't apply at all to your scenario where only the ac wiring from a pole mount enters the building.

DKC


On 2014/6/25, 12:00, Jesse Dahl wrote:
Re-reading this rapid shutdown convo.

Does 10' from the array mean from the modules or the "mount"? What if the array is on a pole, the pole is 15' tall and the inverter is mounted at the base of the pole? Since the array (modules) is 15' from the inverter is rapid shutdown required?

Again, since the title of 690.12 is "On Buildings" is it required for pole mounts where only AC enters the building? Thoughts?

Thanks!


Jesse


On Sat, Apr 19, 2014 at 12:22 PM, Dan Fink <danbo...@gmail.com <mailto:danbo...@gmail.com>> wrote:

    Hi Aaron, boB, Wrenches;

    I think Aaron brings up a good point, and it's certainly
    confusing to me.

    The boldface type heading of 690.12 is "Rapid Shutdown of PV
    Systems on Buildings"

    The body of the 690.12 text begins with "PV system *circuits*
    installed on or in buildings shall....."

    690.2 defines "Photovoltaic source circuit" as "Circuits between
    modules and from modules to the common connection point(s) of the
    DC system"

    and "Photovoltaic output circuit" as "Circuit conductors between
    the PV source circuit(s) and the inverter or DC utilization
    equipment."

    "PV system" from the heading of 690.12 is not defined in 690.2,
    other than that the definition of "Photovoltaic system voltage"
     specifically includes both PV output and source circuits.

    To me the confusing part of 690.12 is "PV Systems on Buildings"
    is that "system" is not defined, and tends to imply rooftop
    arrays. But "PV system circuits installed on or in buildings
    shall....." is pretty clear. I interpret it to mean anything DC
    and PV stuck to the side of building like conduit, etc, or
    running inside....which means it applies to ground-mount arrays
    too if they terminate outside or inside the building.

    What I'm seeing as the easy work-around for us off-grid folk is
    the old "power shed" idea containing battery bank, balance of
    system, inverter etc....just build it within 10 feet of the PV
    array and you're fine.

    Any thoughts?


    Dan Fink,
    Executive Director;
    Otherpower
    Buckville Energy Consulting
    Buckville Publications LLC
    NABCEP / IREC accredited Continuing Education Providers
    970.672.4342 <tel:970.672.4342>



    On Fri, Apr 18, 2014 at 3:30 PM, b...@midnitesolar.com
    <mailto:b...@midnitesolar.com> <b...@midnitesolar.com
    <mailto:b...@midnitesolar.com>> wrote:


        Bill Brooks should probably respond to this also, but reading
        the NEC, it looks like if the wires
        do not go inside the building to run more than 5 feet (as the
        crow flies), the the rapid disconnect
        does not apply.    OR, less than 10 feet from the array IF
        the PV is mounted on that building.

        boB




        On 4/18/2014 1:34 PM, Aaron Mandelkorn wrote:

            The rapid shutdown language is so confusing. When looking
            at the rapid shutdown language, does PV systems "on" a
            building refer to only situations where the array is on a
            building; or does it include DC conductors as well. For
            example, if the DC conductors from a pole mounted array
            run up the side of a building before punching in to the
            inverter, does this require rapid shutdown?  Is this PV
            system considered "on" a building?

            Aaron

            Aaron Mandelkorn
            Owner/Solar Specialist
            Renewable Energy Outfitters
            719-221-5249 <tel:719-221-5249>
            970-596-3744 <tel:970-596-3744>
            www.reosolar.com <http://www.reosolar.com>
            reoso...@gmail.com <mailto:reoso...@gmail.com>



        _______________________________________________
        List sponsored by Home Power magazine

        List Address: RE-wrenches@lists.re-wrenches.org
        <mailto:RE-wrenches@lists.re-wrenches.org>

        Change email address & settings:
        http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

        List-Archive:
        http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

        List rules & etiquette:
        www.re-wrenches.org/etiquette.htm
        <http://www.re-wrenches.org/etiquette.htm>

        Check out participant bios:
        www.members.re-wrenches.org <http://www.members.re-wrenches.org>



    _______________________________________________
    List sponsored by Home Power magazine

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Redwood Alliance

List Address:RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to