To at least partially answer Ray's question about Class-R fuses: Square-D Heavy Duty fused disconnects, commonly used as DC discos for PV arrays and which use Class-R fuses, are only rated for 80% duty. The non-fused HD discos are 100% rated in PV systems. I'm not sure if that is because of the fuse rating or the fuse holder rating though.
Brian Teitelbaum AEE Solar -----Original Message----- From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Ray Walters Sent: Friday, August 22, 2014 6:14 PM To: RE-wrenches Subject: Re: [RE-wrenches] Assembly Protects Conductors? Most combiner boxes, DC rated breakers, and DC rated fuses and fuse holders we use today, qualify as assemblies for the 100% exception (Outback, Midnite, etc.....) so you only have to size the OCP by 125% of short circuit current rating for edge of cloud effects. Since the conductor is sized based on the overcurrent protection, you do not need to size it to 156% of the short circuit current rating, if you take advantage of 100% duty rated breakers and combiners. Also, recombiners are still basically combiner boxes, and so all the same rules apply. The additional 125% is only for breakers that are rated at 80% (most AC breakers for example) . For DC, the only time you would size for the full 156% would be if you were using something like an old QOU breaker, and those aren't rated for high enough voltage for today's arrays anyway. I'm not aware of any other readily available DC rated breaker that is NOT 100% duty rated. Some RK5 fuse assemblies may also not be 100% rated. (Wrench Colleagues please correct me on this....) Basically unless you are using surplus equipment from the stone age, (no offense to my fellow stone age wrenches) you only need to oversize the conductors by 125%. By the time you apply all the other applicable deratings for conduit fill, terminals rated at 75 C, and direct sunlight on roofs (table 310.15B3c) and consider voltage drop, you really don't need to keep oversizing. R.Ray Walters CTO, Solarray, Inc Nabcep Certified PV Installer, Licensed Master Electrician Solar Design Engineer 303 505-8760 On 8/22/2014 2:34 PM, ma...@berkeleysolar.com wrote: > Folks, > > In looking at a circuit breaker based re-combiner for the first time, > I am now pondering the meaning of the Exception below: > > NEC 2014 690.8 (B) Conductor Ampacity. PV system currents shall be > considered to be continuous. Circuit conductors shall be sized to > carry not less than the larger of 690.8(B)(1) or (2). > > (1) One hundred and twenty-five percent of the maximum currents > calculated in 690.8(A) before the application of adjustment and > correction factors. > > Exception: Circuits containing an assembly, together with its > overcurrent device(s), that is listed for continuous operation at 100 > percent of its rating shall be permitted to be used at 100 percent of > its rating. > > Just to be clear, it is only the assembly that can be used at 100 > percent of its rating. (Isc*number of strings*1.25) The conductors in > the circuit still have to be sized for continuous operation > (Isc*number of strings*1.25*1.25). > > I ask because a vendor with a 100% circuit breaker re-combiner states > in their cut sheet that use of the device "allow smaller home run > cable sizes from the string combiner to the inverter". Is anyone aware > of a means by which this claim can be substantiated? > > Thanks, > > Mark Frye > Berkeley Solar Electric Systems > > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist > .html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > _______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.htm l List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org _______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org