Hello Esteemed Wrenches,

I have a prospective client who has an old GTBB system using a Trace SW -- it 
was permitted and signed off by the utility way back when and has been 
operational ever since.  It's a Trace SW 4024 that's feeding the grid through a 
Trace T-240 transformer -- I didn't see a GTI.  All he wants me to do is 
replace his failing array (which would increase his array size from 1152W to 
3300W) -- not pull a permit, not change the BOS other than to add a 2nd charge 
controller.

The original question that lead me to write this post is whether the SW4024 can 
handle the full 4kW sell-back onto the grid -- I couldn't find any specs on 
that on the web.  

But the question I have now is whether the Trace SW is UL1741 compliant.  I 
didn't think to do an anti-islanding test before I left the site.  If it's not, 
then I'm thinking maybe I should insist that he change out his inverter for a 
modern one, or I'll pass on the job.  If it fails an anti-islanding test (which 
I'll do next time I'm in his neighborhood), then the dangers are obvious, and I 
don't want the liability.

What would you all do in this situation?  Do any of you have experience with 
grid-tied SWs -- any advice?

Thanks,

Russ

--
Russell Mueller
NM EE98 Electrical Contractor, license #382671
NM ER1J Journeyman Electrician
Photovoltaic Designer / Installer




BUFFALO SOLAR LLC
Taos, New Mexico
575-770-4877
r...@buffalosolartaos.com





_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to