I agree with Kurt: you need a licensed plumber in your area to advise you, if you're trying to keep the AHJs happy . 2nd, I'm very sure you don't want an exhaust/ combustion type vent under the array. I've had several over the years, and seen some arrays installed over them. They can get fairly hot and put quite a bit of steam out. I would not trust the module backing material to a concentrated long term dose; which module is going to have a problem first?

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 9/24/2014 11:16 AM, Kurt Johnsen wrote:

Should you decide to lower your plumbing vents I have found an inside pipe cutter to be an inexpensive and handy tool. Cut the vent and lead off an inch above your desired pipe height and use the inside cutter to cut the pvc pipe. Go slow and be careful to keep air space between the pvc and lead as the lead will cut very easily.

Also I wouldn't rely on us well intentioned wrenches to make the call on the plumbing code in your jurisdiction. Though the state plumbing codes are usually based on the international code, there will be differences. If you can't pull up your state plumbing code online then ask your plumbing inspector. In Florida the minimum height above a roof surface is 6" (904.1). As for relocating 905.2 states that "all vent and branch vent pipes shall be so graded and connected as to drain back to the drainage pipe by gravity". Table 710.1(1) shows that for 1.5" pipe a slope of ¼" per foot is sufficient to handle 3 fixtures. I would take that to indicate ¼" / foot is plenty for a 1.5" vent.


On Wed, Sep 24, 2014 at 11:20 AM, Dave Click <davecl...@fsec.ucf.edu <mailto:davecl...@fsec.ucf.edu>> wrote:

    Flipping through the '04 plumbing code I see a few slopes called
    out (1/4" per 1' for fixture vents, 1" per 1' for circuit vents,
    1/2" per 1' for combination drain/vent...). Fixture vents have a
    maximum distance of a few feet from fixture trap to vent, but I
    don't think this prevents you from then running that vent
    horizontally. 916.2 states that for vents other than stack vents
    or vent stacks if your vent is >40' you need to upsize the whole
    vent pipe (tough to do for an existing building, of course). Stack
    vents have a "maximum developed length" of 100' for a 1.5" vent
    which should be enough space to get away from under the PV. I
    don't see any slope requirements specifically for stack vents but
    my non-plumber's eye may be missing something.

    The stack vent sizing Table 916.1 appears (in part) here too and
    it looks like the tables match up to a 2.5":
    http://www.engineeringtoolbox.com/drainage-vents-d_1110.html

    DKC




    On 2014/9/24 10:19, Jason Szumlanski wrote:
    I am unable to find anything in the Florida code that precludes
    covering a plumbing vent. The code does require the vent to be 6"
    above the roof surface I believe.

    I was unable to determine if these vents need to be vertical with
    no bends in the attic. Obviously you wouldn't want to create a
    trap in the attic, but a couple of 45's to relocate a plumbing
    vent to accommodate more PV seems like a desirable thing to do
    sometimes. Does anyone know if these can be relocated, i.e. to an
    adjacent roof surface?

    On my own home I had a vent to deal with. I broke out my
    saws-all, split the lead like a banana and peeled it back, cut
    the pipe at an angle, and folded the lead back into the pipe
    after applying sealant between the lead and pipe. There is a 1"
    gap between the rim of the pipe and the back of the module. My
    theory on this working safely is that, a) there will be far less
    rainwater falling in and around this pipe with a module over it,
    and b) it is about 24" from the roof ridge and there is a module
    over it so there will be very little water sheeting down from
    above the vent. Code notwithstanding, I felt this was a solid
    method on my own home, and I have inspected it after 6 months of
    Florida downpours and found no issues.


    Jason Szumlanski

    Fafco Solar


    On Wed, Sep 24, 2014 at 6:38 AM, Bill Loesch
    <solar1onl...@charter.net <mailto:solar1onl...@charter.net>> wrote:


        Bruce, August, et al,

        This is but one more example of confusing terminology. A
        plumbing vent is not an exhaust vent!

        A plumbing vent (what August calls a cold vent) is provided
        to allow the sanitary drain traps (and perhaps more) to
        operate properly. Without the properly functioning traps you
        would have sewer gas smell and sewer gas from the plumbing
        fixtures. This was commonplace when indoor plumbing was
        introduced to early adopters.

        An exhaust vent is another animal entirely. An exhaust vent
        carries the combustion products to a suitable exterior
        location for dilution with ambient air. With the advent of
        power vented combustion appliances, a direct vent (one that
        takes in combustion air from the outside and naturally
        exhausts combustion products to the outside) is IMHO the only
        responsible way to install any power vented appliance in a
        freezing climate. (Power vented appliances come in both
        condensing and non-condensing flavors-they can penetrate the
        side wall or the roof). Originally, two separate pipes (with
        two independent properly separated penetrations) was used.
        That technique is still often used today. More recently
        concentric vents have been introduced both for condensing and
        non-condensing applications. A concentric vent can simplify
        some installations by putting the exhaust pipe inside a
        larger air intake pipe allowing for one, albeit larger,
        penetration. As you might imagine if the exhaust flow is
        hindered/diverted/redirected by an inappropriately located
        solar module combustion gasses will be re-ingested into the
        intake air. Not good for equipment performance. My
        understanding is the power vented _appliance manufacturer_
        dictates what kind of separation/clearances are needed with
        their product. My guess is you find they want at least a foot
        of separation between the top of the " inverted cone" and the
        module. Probably not what you had in mind for an
        aesthetically pleasing installation.

        I hope this helps,

        Bill Loesch
        Solar 1 - Saint Louis Solar
        314 631 1094  <tel:314%20631%201094>

        On 23-Sep-14 6:54 PM, August Goers wrote:
        Bruce and All, Sorry, I hit send before I had a chance to
        complete my thoughts. What I meant to say was that I've
        found AHJs often allow us to cover cold plumbing vents but
        I've never tried or had any luck with covering hot vents
        including condensing boiler PVC vents. Once again, if in
        doubt you could see what the plan checker or inspector
        thinks. Best, August -----Original Message----- From: August
        Goers [mailto:aug...@luminalt.com] Sent: Tuesday, September
        23, 2014 4:15 PM To: 'RE-wrenches' Subject: RE:
        [RE-wrenches] Modules over vents Bruce, I'll send you the CA
        plumbing code vent section offlist (attachment too large for
        this list). The way I read the code is that you technically
        can't cover any type of plumbing or hot vent. However, and
        I've run into little resistance from AHJs in the Bay Area by
        covering these. You might want to check in with your plan
        checker. Best, August Luminalt -----Original Message-----
        From: RE-wrenches
        [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf
        Of Bruce Leininger Sent: Tuesday, September 23, 2014 3:49 PM
        To: RE-wrenches Subject: [RE-wrenches] Modules over vents Hi
        all. We're designing a system on a roof that is literally
        infested with plumbing, exhaust and combustion vents. The
        combustion vents are PVC and none of the vents are more than
        1.5' above the roof. A racking company says that we can
        cover them with modules, since the modules will be at least
        4' above the roof. They have not yet provided any building
        code references to say that this is ok. Do any of you know
        if the building code allows this? Thanks. Bruce




    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org  
<mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm  
<http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org  <http://www.members.re-wrenches.org>



    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to