William,
I see now from the separate post from Michael Kelly of Solectria that indeed you cannot combine your two strings with this inverter. I think that leaves you stuck with four separate disconnect switches unless someone on this list knows of a four pole DC rated disconnect switch. Or, you’ll have to switch inverters. I have never installed these Solectria inverters so I don’t know much about them. Best, August Luminalt *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of *William Miller *Sent:* Tuesday, October 07, 2014 8:28 AM *To:* RE-wrenches *Subject:* Re: [RE-wrenches] TL inverter with long DC Feeder August: I have been told I can't combine upstream of the inverter. William Miller Solar On Oct 7, 2014, at 8:03 AM, August Goers <aug...@luminalt.com> wrote: William, We have bumped into similar dilemmas when needing remote DC disconnects with TL inverters. I believe the Solectria you are using has two MPPTs? Ideally, you would keep each string separate to benefit from the dual trackers – this would mean four DC disconnects if you went with a standard product like a Square D HU361RB. If you combine each of the two strings out at the array(s) then you could get away with two disconnects, one for each inverter. Neither option is ideal. Best, August Luminalt
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org