HI Dan,

Have you tried this on a different power source, say generator etc?
You might also try a different inverter brand just to make sure.

I once had radio noise from a magnum, some years ago.  Tried everything, in the 
end, I swapped it for a VFX and the problem was gone, customer was happy.

And I'm going to agree with Mitsubishi, most likely the inverter.
The OB/FX just isn't compatible with some machines.

jay

peltz power
On Nov 30, 2014, at 4:29 PM, <d...@foxfire-energy.com> 
<d...@foxfire-energy.com> wrote:

> We're still not at the bottom of it. Seems Mitsubishi is doing their level 
> best to finger the RE system. Yes, the current wave form (On a Fluke 43 Power 
> Analyzer) has a shoulder.. looks down right funky on one inverter thru the 
> X240 until the 2nd inverter lights. Current also looks funkular when each 
> mini split is lit (Pulses).. Still, I'm thinking it's more about how the mini 
> splits toke power rather than how the Outbacks produce power. The voltage 
> waveforms look fine.
>  
> the other chin scratcher is that it seems this model of mini split has only 
> been around since spring. There might be a model specific cold weather setup 
> the AC folks missed. Something about a jumper on a control board that needs 
> to be snipped to enable the compressor heater.
> 
> We also noticed that all mini splits work just fine if you leave them on and 
> turned down.. But that kind of power draw for folks that have been loving off 
> grid since 92 is just unacceptable. (these guys were turning off GFI breakers 
> because they could see a draw).
> 
> Either way, the power system itself is working fine as is everything else in 
> the house. And no, the new power system has not kept the lawn mower from 
> starting or the dog from eating the cats food.
> 
> Peace. db
> 
> Dan Brown
> Foxfire Energy Corp.
> Renewable Energy Systems
> (802)-483-2564
> www.Foxfire-Energy.com
> NABCEP #092907-44
> <sigimg0.png>
> 
> 
> -------- Original Message --------
> Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback
> VFX Off Grid
> From: Wayne Irwin <wa...@pureenergysolar.com>
> Date: Tue, October 21, 2014 8:52 pm
> To: Wrenches <re-wrenches@lists.re-wrenches.org>
> 
> We have found that the mini-splits have only had issues while gen sets are 
> running. 
> In some cases (when on genset) the mini's will run irregularly or flash a 
> fault status.
> 
> Rather than try to have the mini's run on gen power we install dc chargers to 
> charge batts from gen power.
> 
> My thought is that the AC Installer either has something wrong or the 
> Mitsubishi's have very tight parameters.
> Be sure that the wiring from the inside unit to the outside unit are correct. 
> Should be only three wires (plus gnd). Very easy to check.
> 
> Possible alternative solution would be look into the cost of installing a 
> Gree since they are the least expensive.
>  
> 
> 
> Wayne Irwin,
> President
> License #CVC56695 
> State Licensed Solar Contractor
> Pure Energy Solar International Inc. 
> wa...@pureenergysolar.com 
> http://PureEnergySolar.com
> http://SolarChargingStation.net
> 352 377-6527 Office
> 352 336-3299 Fax
> 352 316-1637 Cell
> 
> The Sun Is Always Shining!
> 
> The content of this message is Pure Energy Solar Confidential. If you are not 
> the intended recipient and have received this message in error, any use or 
> distribution is prohibited. Please notify me immediately by reply e-mail and 
> delete this message from your computer system. Thank you.
> 
> 
> Date: Tue, 21 Oct 2014 11:23:31 -0600
> From: r...@solarray.com
> To: re-wrenches@lists.re-wrenches.org
> Subject: Re: [RE-wrenches] Mitsubishi Mini Split fighting with Outback VFX 
> Off Grid
> 
> The Outback is not a perfect Sinewave.  It still has tiny steps in the wave, 
> and when electronics have a problem, its usually with the wave form as it 
> crosses zero voltage .  Instead of being instantaneous, it has a few 
> milliseconds of time the wave is at the zero crossing, which can drive some 
> electronics nuts.  I don't understand the issue beyond that, but apparently 
> the electronics use the zero crossing for timers and synchronizing, and 
> they're looking for an instant "click", not a smear.  
> Do the heat pumps work with the generator?  Even though generators can have 
> more harmonic distortion, they do usually have a clean zero crossing.
> If this is the case, I'm afraid I don't have a cure.  We used to use 
> capacitors, but Dan from Exeltech just poo pooed that fix in another recent 
> thread, so I don't have any other tricks up my sleeve.
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer, 
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> On 10/21/2014 8:54 AM, d...@foxfire-energy.com wrote:
> Anyone else had issues with Mitsubishi Mini Split heat pumps fighting with 
> Outback VFX off grid inverters? Everything is brand new. Outback VFX7248, 
> three separate heat pumps. The heat pumps shut down reporting multiple / 
> confusing input commands. The heat pump guys want to blame the power system. 
> I'm thinking bad Sushi. Thanks db
> 
> 
> Dan Brown
> Foxfire Energy Corp.
> Renewable Energy Systems
> (802)-483-2564
> www.Foxfire-Energy.com
> NABCEP #092907-44
> <ATT00001.png>
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> _______________________________________________ List sponsored by Redwood 
> Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver 
> email address & settings: 
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update 
> participant bios: www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to