Having the LVD be temperature compensated so that the load is always
disconnected above the freeze point of the battery would be a Huge
Improvement on the whole concept of LVD. In combination with State of
Charge monitoring, like the Whiz bang Jr, would be the most effective,
and just program the disconnect to stay above freezing for a typical
lead acid battery. I got this from a Trojan White Paper:
R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760
FLA batteries will freeze easier if they are discharged. I suppose
that you could
use the battery temp sensor to make sure you charge them up good when
the temp gets cold enough.
boB
_______________________________________________
List sponsored by Redwood Alliance
List Address: [email protected]
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/[email protected]/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org