Luke,

For reference, we sold/installed many hundreds of Uni-Solar products since 
2002. I have never seen anywhere near that much Voc loss. 

Since the PVL-68 has an open circuit of 23.1V (92.4V) but you only see 14.2V 
(71V), a loss of 25%, I do not believe degradation is the culprit even at 15 
years. The rated degradation is 0.73% per year. That should put you at 82.3 
Voc. But, Uni-Solar consistantly outputs  at least 10% more than rated power, 
even with age it should be higher than 82 volts.

Proper Uni-Solar installation required 2 screws into the roof up near the top. 
A misplaced screw and time or an open seam may be causing a ground fault, 
pulling down the voltage of the array. Start by using a Megger at the combiner 
to check for leakage. No one likes crawling in a hot attic but I think you may 
need to. 


Larry Crutcher



Hello Off-Grid Wrenches,

I recently made a periodic maintenance visit to a residential off-grid system I 
take care of here in Southern CO, and discovered an interesting problem. 

This system has an array of 48x Uni-Solar PVL-68 laminate modules applied 
directly to standing-seam metal roofing. 

The data logging on the controller (Outback MX-60) indicated that the system 
was having trouble completing a charge cycle and going to float. Initially I 
assumed was due to heavy electrical use by the occupants (renters). After a 
little checking, I noticed that the module string voltage was only about 0.5V 
above the battery voltage! 
This was a cool late morning, with full sun, and the array was charging almost 
2kW at 54.5V. The module strings were running at 55V. I've noticed the module 
voltage being lower than I'd like before, but it has never been this low. I 
suspect this is the real reason the system hasn't been able to complete a 
charge cycle.

By removing the loads I was able to get an open-circuit voltage of 71V, but 
that still seems pretty low. 

Has anyone else experienced a voltage degradation issue with the Uni-Solar 
laminate? What was the expected annual voltage degradation for this technology? 

These modules do have some age on them. The system was installed about 15 years 
ago (by a competent installer who is now retired). The system was installed 
before MPPT controllers were common, so I assume the modules are wired in 
strings of 4 for 48V nominal. 

Any experiences or opinions are appreciated.
Thanks in advance. 

-Luke


Luke Christy

NABCEP Certified PV Installation Professionalâ„¢: Certification #031409-25 
NABCEP Certified Solar Heating Installerâ„¢: Certification #ST032611-03       
CoSEIA Certified PV Installer 

Solar Gain Services, LLC
PO Box 531
Monte Vista, CO. 81144
[email protected]
719.588.3044
www.sgsrenewables.com <x-msg://40/www.sgsrenewables.com>

  





_______________________________________________
List sponsored by Redwood Alliance

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/[email protected]/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to