Your assumption is the rule here. Metal inside a building envelope and it 
cannot transition at the penetration it must be metal before entry.

----------------------------------------------------------------------------
Dana Orzel 
Great Solar Works, Inc -  NABCEP # 051112-136
E - d...@solarwork.com  - Web - solarwork.com 
O - 970.626.5253  C - 208.721.7003
"Responsible Technologies for Responsible People since 1988"  
 Please consider the environment before printing this email.



-----Original Message-----
From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Christopher Warfel
Sent: Monday, July 13, 2015 10:59 AM
To: re-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] DC conductors in metallic raceway/conduit

I was under the assumption that dc conductors could only be run inside a 
building when in metallic raceway/conduit (up to a readily accessible 
disconnect switch) .  The building being occupied/residence.    A 
contractor ran 5 feet of pvc from the wall penetration to the charge controller 
in a concrete block garage.  I don't see anything that allows this by what I 
find in the NEC. Has anyone have a reference that permits this?  Thank you for 
any assistance.



--
Christopher Warfel, President
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to