Jerry,

A long distance wire run is practical now days using a high voltage controller. 
Have a look at Schneider and Morningstar 600Vdc controllers. Not sure what you 
mean "by nothing can be changed but wire size” but you will have to rewire the 
strings into series and protect the wire run.

Larry Crutcher
Starlight Solar Power Systems



On Jul 22, 2015, at 10:37 AM, Jerry Shafer <jerrysgarag...@gmail.com> wrote:

Wrenches
Some time back there was discussion on the conductor size and efficiency rating 
requirement for long DC runs.
What I am looking at is this, 400 feet of MCM 400 to keep the line loss at or 
below 1% per NEC code for an off grid application, cost vs return is not 
acceptable. 2/0 is less than 2.5% and the cost is far less. Specs are 4 strings 
of 3, 250 watt modules feeding one Outback FM 80 charge controller. There are 
lots of things I can do like SMA instread, or 200 VDC charge controller but 
nothing can be changed except the wire gauge. Does anyone recall a thread with 
this topic.

thoughts ??
Jerry