Jarmo,


Unfortunately, simple is wrong in this case—and detrimental to the PV industry 
that needs all the roof real estate it can find.


Bill.



Bill Brooks, PE

Principal

Brooks Engineering





From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of jarmo.venalai...@schneider-electric.com
Sent: Tuesday, July 28, 2015 10:43 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Using the North Facing Roof



Hi:

Granted that the description is very simple, but that is the intent.

The essence of it is that the "loss" for small variations in angle of incidence 
is approximately bounded by, (less than), the sin of the angle between the 
orientations of two panels/arrays in question.

10 degrees --->  minus 17%
20 degrees --->  minus 33%
30 degrees --->  minus 50%

If you go through the detailed math and take into account  atmospheric effects, 
especially when the sun is near the horizons, temperature, location, weather, 
etc., the result will vary, but will not be worse than the sin of the angle.

I'll draw out better picture with more detail for Vancouver.  We're at a fairly 
high latitude, so overall array orientation is a more sensitive factor than 
farther south.

JARMO

_____________________________________________________________________________________

Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
Sales Application Engineer
Phone: +604-422-2528  |   Tech Support: 800-670-0707  |   Mobile: +604-505-0291
Email:  <mailto:jarmo.venalai...@schneider-electric.com> 
jarmo.venalai...@schneider-electric.com  |   Site: <http://www.xantrex.com/>  
www.Xantrex.com  |   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1







*** Please consider the environment before printing this e-mail





From:

Brian Mehalic <br...@solarenergy.org <mailto:br...@solarenergy.org> >


To:

RE-wrenches <re-wrenches@lists.re-wrenches.org 
<mailto:re-wrenches@lists.re-wrenches.org> >,


Date:

07/28/2015 09:48 AM


Subject:

Re: [RE-wrenches] Using the North Facing Roof


Sent by:

"RE-wrenches" <re-wrenches-boun...@lists.re-wrenches.org 
<mailto:re-wrenches-boun...@lists.re-wrenches.org> >



  _____




The analysis of 50% of south facing production is too simplistic; running some 
modeling shows that, depending on the latitude, the difference can be much 
smaller, approaching 25% less for the north facing.  I think this layout could 
become more common especially on low slope commercial roofs, where the north 
facing module would occupy space that was already unused due to interrow 
shading.  Of course the closer to the equator the less difference between 
production of the north and south arrays...and you better be careful when 
stringing them in series so as not to mix N and S facing..plus filling in all 
those gaps between rows could make servicing the array a bit problematic!

Cheers,


Brian Mehalic
NABCEP Certified Solar PV Installation Professional™ R031508-59

PV Curriculum Developer and Instructor
Solar Energy International
http://www.solarenergy.org <http://www.solarenergy.org/>

On Tue, Jul 28, 2015 at 10:24 AM, <billbroo...@sbcglobal.net 
<mailto:billbroo...@sbcglobal.net> > wrote:
Jarmo,



The sun’s geometry is not nearly that simple. To understand the impact of 
north-facing arrays, you have to perform a simulation. PV:WATTS does this just 
fine and it is easy to show that a 18-degreed North-facing tilt produces 75% of 
a perfect 30-degree south-facing array. Far more than your assumption of 50%.



To compare 15-degrees South to 15-degrees North, the numbers are slightly 
better at 77%. We are going to see a lot of north-facing arrays once people 
understand that low tilt angles are very forgiving on North slopes. Steep 
slopes are a totally different story and you have to run the numbers….



Bill.



From: RE-wrenches [mailto: <mailto:re-wrenches-boun...@lists.re-wrenches.org> 
re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of  
<mailto:jarmo.venalai...@schneider-electric.com> 
jarmo.venalai...@schneider-electric.com
Sent: Tuesday, July 28, 2015 8:04 AM
To: RE-wrenches < <mailto:re-wrenches@lists.re-wrenches.org> 
re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Using the North Facing Roof



I did a slide on the effect of North facing modules.  For even a fairly 
aggressive rotation North as shown, the effect is "only" a 50% reduction.

The questions of whether or not to do it, are,

- is the mounting structure simpler, lower cost
- security against wind
- can I put a larger array on the roof  (typically yes, if you make back to 
back pyramid shaped structures)
- overall, what is the cost versus benefit

JARMO
_____________________________________________________________________________________

Jarmo Venalainen  |   Schneider Electric   |  Xantrex Brand  |   CANADA  |   
Sales Application Engineer
Phone:  <tel:%2B604-422-2528> +604-422-2528  |   Tech Support:  
<tel:800-670-0707> 800-670-0707  |   Mobile:  <tel:%2B604-505-0291> 
+604-505-0291
Email:  <mailto:jarmo.venalai...@schneider-electric.com> 
jarmo.venalai...@schneider-electric.com  |   Site: <http://www.xantrex.com/>  
www.Xantrex.com  |   Address: 3700 Gilmore Way, Burnaby, BC V5G4M1


 <http://www.xantrexrebate.com/>


 <http://www.xantrex.com/>

 <https://www.facebook.com/Xantrex>

 <https://twitter.com/Xantrex>

 <https://twitter.com/Xantrex>




*** Please consider the environment before printing this e-mail


From:

"Peter Parrish" < <mailto:peter.parr...@calsolareng.com> 
peter.parr...@calsolareng.com>


To:

"'RE-wrenches'" < <mailto:re-wrenches@lists.re-wrenches.org> 
re-wrenches@lists.re-wrenches.org>,


Date:

07/28/2015 12:22 AM


Subject:

[RE-wrenches] Using the North Facing Roof


Sent by:

"RE-wrenches" < <mailto:re-wrenches-boun...@lists.re-wrenches.org> 
re-wrenches-boun...@lists.re-wrenches.org>



  _____




I recently read a short piece that caught me up short, and I quote:

“The fast dropping cost of solar, while a huge boon to the adoption of solar 
PV, has counter-intuitively altered design parameters. No longer is the 
north-facing roof considered unusable because limited application in less-than 
optimal orientations can still show a positive net benefit. Arrays are thus 
designed now with elements or sub-arrays in these locations, increasing overall 
kW installation while reducing the energy production per capacity installed. 
This might have been anticipated based on sheer economic analysis from a users 
perspective, but so long has solar been expensive that these less optimal 
orientations were never seriously considered.”

I doubt that the individual who wrote this piece came to these conclusions 
him/herself. Does anyone know of a recent article that argued this perspective? 
Is this an emerging design practice? If so, I’d like to know more about it.

-          Peter

Peter T. Parrish, Ph.D.
President, SolarGnosis
1107 Fair Oaks Ave., Suite 351
South Pasadena, CA 91030
 <tel:%28323%29%20839-6108> (323) 839-6108
 <mailto:peter...@pobox.com> peter...@pobox.com



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
_____________________________________________________________________________________________________________________
List sponsored by Redwood Alliance

List Address:  <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
 <http://www.members.re-wrenches.org/> www.members.re-wrenches.org



  _____


This email has been checked for viruses by Avast antivirus software.
 <https://www.avast.com/antivirus> www.avast.com



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>




______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
_____________________________________________________________________________________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org 
<mailto:RE-wrenches@lists.re-wrenches.org>

Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:  
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org






---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to