I know that IF the SMA SI  master inverter is shut down then all follow, shunt 
trip breaker only for the master? Also look at the Midnite MNBCB 1000/50
(Previous Model Num: MNBCB-1000/50-Battery Combiner)
MidNite 1000amp battery combiner box
Includes a 1000amp Positive and Negative bus bar with 3/8 inch studs.
On Aug 26, 2015, at 3:39 PM, Ray Walters wrote:

> Hi Wrenches;
> 
> I have an upcoming project to be inspected, ,and having spent too much time 
> on off grid and out of country work, I'm now playing catch up with the new 
> 690.12 and 690.71(H) requirements.
> The proposed GTB system is 3 Radians with a ground mounted 18kW array and 
> large HUP battery bank.  I just read a Bill Brooks article that basically 
> says that Rapid Shutdown not only applies to ground mounted arrays that come 
> into buildings, but also applies to battery cables if longer than 5 ft.
> There are 690.12 compliant combiners from Midnite that work with their 
> Birdhouse system, so I think I've got a handle on the array requirements 
> (more or less).
> What is stumping me is how to feed three 8kW inverters from a large battery, 
> and install auto disconnect breakers within 5 ft.
> 1) the disconnect has to be large enough, Midnite only makes a 250 amp remote 
> trip breaker, so I'd have to parallel 3 of these?
> 2) 690.71(H)3 says the breaker can't be in the battery enclosure, which is 
> tricky since the enclosure is 160" long from one end to the other with 2 
> parallel strings.
> 3) I'm having trouble even finding an enclosure for 3 large DC breakers (Flex 
> 1000 is the only thing I know of) and to get the enclosure close enough is an 
> issue too.
> I just got off the phone with Tech support at Outback and they don't seem to 
> have any Rapid Shutdown gear ready.
> Are inspectors actually requiring this yet, or because of the lack of 
> available UL listed products, can we take a pass on at least some of the 
> requirements?  Another strategy the Outback tech thought of is to put all the 
> equipment into a shipping container and then its not in or on a "building", 
> and 690.12 doesn't apply.
> 
> -- 
> R.Ray Walters
> CTO, Solarray, Inc
> Nabcep Certified PV Installer,
> Licensed Master Electrician
> Solar Design Engineer
> 303 505-8760
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 

> t...@swnl.net               www.SWNL.net
>                 Solarwinds Northernlights       
>        Serving Mid Coast Maine & Northern California
>                          207-832-7574   Cl. 610-517-8401                      
>         
>                               Blair "TUMP" May
>                ********  MAINE'S CHARTER ********
>                       NABCEP    "Certified PV Installer" 
>    
>               ********  MAINE'S CHARTER ********
>                   Trace Xantrex "Certified" Dealer / Installer"
> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to