David, 
Windy's system sizing spreadsheet was first developed in the 1990s or so, when 
PV was expensive and lead (and copper) were relatively cheap. In those days, 
"one panel per battery" was a standard rule of thumb -but panels were seldom 
more than 55 watts, so 110 watts (6 1/2 A) was about standard for a pair of 
golf carts. That's a C/34 charge rate, max. 

This past spring Windy and I revised that spreadsheet to reflect modern sizing 
and economics. It now works with any module cell count, for example. Contact me 
off list if you'd like a copy. (Be patient for the reply as I'm currently 
traveling.) 

> On Sep 15, 2015, at 6:04 PM, "Dave" <d...@independentpowerllc.com> wrote:
> 
> The AEE catalog battery sizing template works well as it allows you to dial 
> back the days of autonomy needed. As I remember the old Dankoff Solar battery 
> sizing method pushed the watt hour size of battery banks to large, and 
> expensive, levels.
>  
> The collective experience of this group, and others, has emphasized designing 
> off grid pv system's where the primary consideration is ample PV array sizing 
> and where the storage battery is sized in the C/10 range. With lower module 
> prices this has been practical for a few years now and it has been 
> demonstrated that smaller watt hour battery banks have proven to be not only 
> cost savers but also perform well for years as they live in a system where 
> they are very likely to be fully charged on a regular basis.
>  
> Even here in northern Vermont where we experience late fall and winter daily 
> peak sun hours in the 1 hr/day average range, designing large battery banks 
> has been frowned on for many years out of my shop. Oversize the pv array and 
> run the generator when needed.
>  
> David Palumbo
> Independent Power LLC
> 462 Solar Way Drive
> Hyde Park, VT 05655
> 802-371-8678 cell
>  
>  
>  
> From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On 
> Behalf Of Chris Mason
> Sent: Tuesday, September 15, 2015 5:39 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] Battery bank calculator
>  
> Homer can do it but it is expensive.
> http://www.homerenergy.com
> 
> On Sep 15, 2015 9:31 AM, "RE Ellison" <reelli...@gmail.com> wrote:
> I don't think it can be done accurately with a sizing tool i've actually 
> never heard of a tool at least not that I can remember
> 
> There's far too many variables.
> Everything from loads to solar isolation as well as the habits of the 
> individual occupants and the appliance selection in the home
> 
> The old joke used to be calculate what you needed for three days and then 
> double it as far as battery bank size
> 
> Just a few thoughts, batten five dollars will get your cuppa coffee and a lot 
> of convenient stores
> 
> Bob Ellison
> 
> 
> 
> > On Sep 15, 2015, at 9:21 AM, gary easton <g...@arp-solar.com> wrote:
> >
> > anyone have a suggestion for a battery bank sizing tool?
> >
> > --
> > Sent from Gmail Mobile
> > _______________________________________________
> > List sponsored by Redwood Alliance
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Change listserver email address & settings:
> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive: 
> > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out or update participant bios:
> > www.members.re-wrenches.org
> >
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org