Having DC and AC in the same trench (but in separate conduits) is acceptable in 
the NEC, the conduit itself is all the separation required by the NEC. 

 

That being said, I would also not worry about twisting DC wires or ensuring any 
special distance between conduits based on concerns of electro-magnetic noise 
between conductors. If you are talking about a system with a third party arc 
fault detection/interruption system (like AFCI combiners, not a string inverter 
with built in AFCI). I have not run into it yet, but I have heard that the 
third party AFCI combiners are known to nuisance trip due to noise in the wires 
(mostly from the inverter is what I’ve been told). So anything you can 
reasonably do to prevent more noise in the DC side of things, why not do it. I 
would not go so far as to try to twist a set of 3/0 copper conductors in a 200’ 
conduit pull though J I’d rather just bump my conduits up one trade size across 
the board to push my wires farther apart. Since EMF’s decay in strength by the 
square of the distance (2x the distance equals ¼ the emf) just upping the PVC 
conduit sizes makes it simple to significantly reduce any potential emf.

 

All the above is moot though if we’re talking small wire/currents. 

 

Generally most people don’t think about separating AC and DC conduits in a 
trench, and I have not yet heard of an instance where it has caused a problem. 
I over think most things, just to sit back and bring myself back to planet 
earth where I say “ Put AC and DC in separate conduits, try to keep them 
separate in the trench if you can do so easily, then bury it and walk away”. 

 

With Regards,

 

Daniel Young, 

NABCEP Certified PV Installation ProfessionalTM: Cert #031508-90

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Benn Kilburn
Sent: Wednesday, October 07, 2015 11:22 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] DC conduit with AC secondary?

 

Adam,
My Canadian Electrical Code requires "separation" between conductors of 
different "systems".  I believe the NEC is the same/similar.  
You may notice a flimsy (yet stiff) paper(?) barrier between the AC and DC 
wiring areas in some AC/DC inverter disconnect enclosures.... assume this is 
sufficient as the inverter (should be) certified as such.
In a raceway or "gutter" box, i've been given the ok from electrical inspectors 
to bundle and keep the AC and DC wire bundles separate from each other.
In a trench, since you are running separate conduits, that could be sufficient, 
otherwise the separation could easily be a layer of dirt or perhaps a pressure 
treated plank.

Good Luck.




Benn Kilburn 

Partner, CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy 
Inc

6706 – 82 Ave NW | Edmonton, AB | T6B 0E7

M: 780-906-7807 P: 780-474-8992 | F: 888-405-5843 |  
<http://www.skyfireenergy.com/> www.skyfireenergy.com

 <mailto:b...@skyfireenergy.com> email  
<https://www.facebook.com/SkyFireEnergy> facebook  
<https://twitter.com/SkyFireEnergy> twitter  
<https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5>
 linkedin  <https://plus.google.com/+SkyFireEnergy/> google

 SkyFire Energy Logo_horizontal 
<http://www.skyfireenergy.com/wp-content/uploads/2014/07/SkyFire-Energy-Logo_horizontal.png>
 

 

On Mon, Oct 5, 2015 at 8:45 AM, AE Solar <autonomousenerg...@gmail.com> wrote:

Wrenchers,

Anyone know of code violations associated with running DC conduit in the same 
trench as conduit for AC secondary? Is that allowed? Bad practice even if 
allowed?Thanks

Adam




Adam Katzman
Autonomous Energies
4872 State Route 9G 
Germantown NY, 12526
www.autonomousenergies.com
(518) 567-1468 <tel:%28518%29%20567-1468> 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



 

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 2015.0.6140 / Virus Database: 4435/10774 - Release Date: 10/07/15

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to