Howie,
A Fan Test is described in the T80 user Manual;Page 26;5M(misc.section).
This is a simple Fan test to toggle Fan ON/OFF;Most likely it will turn Fan ON to full speed.
(Based on their Manual).
For a Real-World test(If there is enough current passing through C.C.);
Cover heat-sink/C.C. to prevent airflow through heat-sink.
Wait for temperatures to rise and monitor;Fan will come on and ramp-up from a low speed to it's highest speed.
If this is left in this condition long enough;once the Fan has reached it's highest speed the C.C. should go into a Derate mode and start backing-off the amount of current moving through it.
When C.C. is in Derate mode there should be some type of indication of this presented on the C.C. display.
If time does not permit;use a Heat-gun and gradually heat-up the heat-sink.
Use caution;do not overheat any components etc.
If you do not have experience in doing this type of "experiment" I would not advice doing this.
Hope this helps.
Louis Segarra
Tech.Department/Field Service
Solar Cowboyz
Cell#916-212-0282
-------- Original Message --------
Subject: [RE-wrenches] Apollo charge controller
From: Howie Michaelson <ho...@suncatchervt.com>
Date: Mon, October 05, 2015 7:34 pm
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
HowieDoes anyone have a decent way of checking whether the cooling fan in an Apollo T80 is working properly? It is a variable speed fan, but appears to be a bit challenged (making noise, moving somewhat slowly...Thanks,
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________ List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org