Garrison,
I'm here in a campground in the Emerald Triangle with Jeff Spies, who works for Quick Mount PV, and so I read him your message. He suggested that you take the engineering specs from UniRac and IronRidge to the AHJ, showing her pullout and shear capacities and calculate both for your site, including snow and wind loads. The maximum applied load should be less than the published working load rating.

If the AHJ doesn't accept this approach, the next step is to get a structural engineer to review the same and wet-stamp the result.

This legitimately gets around the manufacturers' certification issue on an individual case basis.

Allan

Allan Sindelar
al...@sindelarsolar.com
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
505 780-2738 cell

 

On 10/15/2015 1:50 PM, Garrison Riegel wrote:

Thanks for the responses. 

 

I called UniRac and IronRidge who both confirmed they max out at 45°.  UniRac said anything over 45° is considered a wall and requires different testing and certification.  They said the primary concern is the end clamp which holds the module by friction only.  Mid clamps should hold no problem.  They suggested getting an engineer to stamp a custom bolted end clamp solution and we should be good.    

 

I’ve been looking for a good excuse to try Snap n Rack…

 

Thanks,

Garrison       

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Aram Alexander
Sent: Wednesday, October 14, 2015 7:39 PM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Racking for Steep Roofs

 

Pro solar will work just fine.

Aram 


On Oct 14, 2015, at 2:56 PM, Jerry Shafer <jerrysgarag...@gmail.com> wrote:

I would suggest calling unirac as it may be a software issue that uou are having but they will confirm eitherway
Jerry

On Oct 14, 2015 9:25 AM, "Garrison Riegel" <garri...@solarserviceinc.com> wrote:

Wrenches,

 

Can anyone recommend a flush mount racking system for really steep roofs?  I have two projects coming up on 15/12 (~51°) and none of the usual manufacturers we use for flush mounts (IronRidge XR, Unirac SolarMount, Schletter Solo, DPW Powerrail) can handle this apparently…at least according to their design tools and manuals.

 

Any advice would be much appreciated.

 

Thanks,

Garrison

 

Garrison Riegel

PV Operations Manager | Solar Service Inc

[p] 847-677-0950 | garri...@solarserviceinc.com

 

NABCEP Certified PV Installation Professional™

 

 

   


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to