An update on this issue:
On my initial visit to diagnose this problem I changed the AGS settings
higher volt start and % state of charge start.  The report from the client
is that this has fixed the AGS issue.  So now I am just dealing with the
100 amp breaker tripping.

The trip time from the client is when the sun hits the panels and once
reset for the day it will not trip until the next morning. What could cause
this?

You are all right that the first step it changing out that breaker that
will be the first on the list when I am back on site.  I hope that is the
only issue because as usual this system is 2 Hrs from the shop with no cell
or internet coverage.
Thanks for your input.
Cheers-
Daniel

Daniel Tittmann
CTO
Greenwired
www.greenwired.com
dan...@greenwired.com
707-923-2001 (office)
707-206-5088 (Cell)

On Mon, Oct 26, 2015 at 10:25 PM, Mac Lewis <maclew...@gmail.com> wrote:

> Hi Daniel,
>
> Do you know what the error is on the AGS? What are the start set points
> that you have? Jay could be on to something if the battery voltage is
> collapsing before the generator can start, the cc current could be high. Do
> you know specifically what time of day the breaker is tripping?
>
> I'd check the Midnite logs and consider starting the generator sooner.  Is
> there large voltage swings (this could indicate bad battery or large load)?
> Make sure the wire is cleaned and torqued properly onto that breaker.
>
> How big is the battery bank and what is the tilt and azimuth of the panels?
> On Oct 26, 2015 11:05 PM, "Jay" <jay.pe...@gmail.com> wrote:
>
>> Hi Daniel
>>
>> Is this a new classic with OCP? Or maybe they don't have it anymore?
>>
>> What it sure sounds like like is a big load on the batteries, it hits
>> faster than the AGS can start, and the caps in the classic are dumping into
>> the super low battery voltage. If this is happening in the AM, guessing
>> with enough light to get the CC alive
>>
>> If there is a trimetric, you can measure the lowest voltage which should
>> give you some good info. Super low volts might mean a bad battery or too
>> big a load or both.
>>
>> But I don't believe it's the other way around that the classic is causing
>> any issues with the AGS/inverter
>>
>> You could always try another CC and see what happens
>>
>> Jay
>>
>> Peltz power
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> On Oct 26, 2015, at 6:30 PM, Daniel Tittmann <dan...@greenwired.com>
>> wrote:
>>
>> Hive mind-
>> hoping you all can help me solve this mystery issue.
>>
>> System:
>> Magnum double panel with Parallel stacked 2x4448 pae inverters.
>> Classic 150 charge controller wired with an NMEPV 50 (din rail) and
>> NMEPV100
>> 18 - 245 watt solar modules (6x3). (not over powered)
>>
>> Issue:
>> every morning the 100 amp din rail breaker is tripping.  from what I can
>> gather simultaneously the magnum RTR shows the AGS go into error.  Re set
>> the breaker and the solar works fine for the rest of the day.
>>
>> Not 100% sure the AGS has worked (under normal operation) at all other
>> than at commissioning and recent testing.
>>
>> Of course on site i cant get it to fail.
>>
>> Tested the AGS by setting start voltage to 48.2 vdc and put the system
>> under load....... voltage drops and generator turned on with no pv-> Batt
>> breaker issue.
>>
>> last visit, chasing one theory, I re routed the battery + from the
>> mnpv100 directly to the battery  + terminal as opposed to the battery + bus
>> bar in the inverter panel still didn't solve the problem.
>>
>> I cant figure out if it the classic causing the issue or if it is the
>> inverters and the AGS.
>>
>> Any input would be appreciated.
>> Thanks
>> Daniel
>>
>> Daniel Tittmann
>> CTO
>> Greenwired
>> www.greenwired.com
>> dan...@greenwired.com
>> 707-923-2001 (office)
>> 707-206-5088 (Cell)
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to