That new chart is for a single block, but we would want the M100 or M110 which is 12 of those S30 blocks connected together (580 AH @ 20 hr rate). I haven't tried them, but I penciled out the ROI and at 3000 cycles they stand up well against other lead acid batteries. 40 v is low, but I believe most inverters can be set to LVD at 40.
Magnum for instance can go as low as 36 v on a 48 v  nom. setup.
I agree with Dan that the minimum temp is a problem for many remote applications.

R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer,
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/29/2016 11:52 AM, Dan Fink wrote:
I second Larry's concerns about Aquion's SOC/voltage curves and tripping LVD at only 40% DOD with standard PV equipment, tied in with not being able to handle high discharge C-rates and surge loads. I did some math on running a typical off-grid home with a well pump on Aquions, and it wasn't pretty, but I may not have done the math right. Very interested to hear personal experience on off-grid homes with these batteries.

I was starting to envision applications for remote MET tower, repeater tower etc applications with low discharge C-rates and high charging C-rates, and then saw Aquions lowest operation temperature of -5C, 23 F. That's considered a "heat wave" during certain times of year in many areas, including here in sunny Colorado. In these applications the batteries are NOT in a heated room, instead an outdoor enclosure at the base of a tower.

AGMs are serving us here just fine on these sorts of esoteric installations, and they have no problem with -29C and lower when kept at high SOC. And, cheap, easy to replace, and giving us many years of life. The ROI math on the Aquions compared to AGM is not adding up for me on these applications.

My only experience with Aquion was their class at the NABCEP conference last year.

Any ground truth experience and stories on Aquions and other similar technologies appreciated here also.

Best regards;

Dan Fink
Adjunct Professor, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Accredited Continuing Education Providers™
970.672.4342 <tel:970.672.4342>


On Fri, Jan 29, 2016 at 7:55 AM, Starlight Solar Power Systems <la...@starlightsolar.com <mailto:la...@starlightsolar.com>> wrote:

    I too am interested in anyone that has installed these. I had some
    concerns back on Nov 10, 2014. Here is a copy/past from that
    conversation:

    Something does not add up to me. The cell has a voltage discharge
    curve way outside that of RE equipment, 1.75 Vpc down to 0.5Vpc. I
    can't see how this technology could be scaled to RE applications
    without wasting much of the capacity. From what I see, only about
    40% could be used before LVD.

    And this:
    The Aquion battery claims their 2.4kWh, 48 volt stack operates
    from 59 to 30 volts. Many inverters have a LBCO of 1.75 Vpc (42
    volts). Depending on voltage sag, that means about half of the
    capacity of the Aquion battery can't be used. Even if the outback
    can operate down to 1.5 Vpc, you are still not able to use the
    full capacity of the battery unless your load is less than 800 Watts.

    I have reviewed their technical presentation and it looks to me
    like the capacity simply can't be used in the off grid
    environment. If you can't use it, why do they rate it at 2.4kWh?
    BTW, the Voltage vs.Energy chart on the spec sheet does not match
    the first chart I posted.







    On Jan 29, 2016, at 7:30 AM, Chris Schaefer
    <ch...@solarandwindfx.com <mailto:ch...@solarandwindfx.com>> wrote:

    To All,
    Great insight on the lithium movement. I do am looking for anyone
    dealing with the new Aquion batteries. I’ve got a couple of
    potential clients that have inquired about them. Saw them at a
    NABCEP training session last spring and while the idea is moving I
    wasn’t impressed. Perhaps it’s time to start a new thread, “Aquion
    batteries”.
    Thanks,
    Christopher
    *From:*RE-wrenches
    [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On Behalf Of
    *d...@energysolarnow.com <mailto:d...@energysolarnow.com>
    *Sent:* Friday, 29 January, 2016 00:49
    *To:* Dan Fink
    *Cc:* re-wrenches@lists.re-wrenches.org
    <mailto:re-wrenches@lists.re-wrenches.org>
    *Subject:* Re: [RE-wrenches] LiFePO4; WAS Availability of
    Powerwall Batteries
    Thanks for sharing your experience with these batteries, Dan.
    I have similar SOC issues with an off-grid customer who has the
    Aquion Hybrid Ion batteries.
    It has difficulty reaching full charge from solar, requiring the
    genny to kick on each morning even in the summer.
    This is even worse in cold winter weather.
    Your explanation of the change in Peukert's exponent above 80% SOC
    with NiFe batteries sounds like what is happening here as well.
    Do you have any experience with Aquion batteries that you can share?
    Thanks
    Don Barch
    Energy Solar
    d...@energysolarnow.com <mailto:d...@energysolarnow.com>


    _______________________________________________
    List sponsored by Redwood Alliance

    List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>





_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to