I'm looking at two Eaton PV250 inverters that failed simultaneously as far
as we know (not my install). Everything checked out normal, but no display
and no power output. I suspect both boards are bad. Upon digging into the
scenario I discovered that the owner had a whole-house generator transfer
switch installed a while back, after the PV was installed. The PV is a load
side interconnection, so calamity should have been expected.

What are the odds that the generator caused the inverter boards to fail? I
was always under the impression that it was more likely for a generator
component to be damaged than an inverter component in this scenario. It
could be coincidence and the inverters may have just failed around the same.

Note:  ~10kW PV, 25kW Generator

Side note: The PV was interconnected at a 50A breaker on a 200A bus bar in
the main distribution panel and somehow passed inspection by an AHJ that
shall not be named... Over 120%, and also not the correct OCPD rating
anyway for these two inverters. Passed plan review and inspection...
Contractor out of business... surprise!