HI Allan,

I’ll let you do the AC or DC couple choice.
However my suggestion if you do DC couple is to go Schneider for all.  Then you 
will have an integrated DC couple package.  Metering and control, they have new 
battery meter and full online capability. 

And one of the things I don’t like about the moringstar is that manual relay.  

You should be able to configure a relay to turn off the GT inverter and turn on 
the 600v CC automatically in the event of a power failure.
Not that I’ve looked for a 80 amp 600vdc one.  

jay

peltz power


> On Jan 30, 2016, at 2:21 PM, Allan Sindelar <al...@sindelarsolar.com> wrote:
> 
> Wrenches,
> I am serving as a consultant for a homeowner with an array of solar equipment 
> that doesn't do what he wants, a common story. He wants independence in the 
> event of an extended utility outage. To cut to the chase:
> 
> He has one array of 3,100 watts feeding through a controller into a 48V 
> battery bank. No issues with this.
> A second array of 4,230 rated watts (2 9-module strings of 235W Sharp 
> modules) currently feeds a Fronius IG-4000 inverter and the grid. In the 
> event of an outage this system shuts down, of course. He is looking at 
> replacing his existing pair of old SW5548s with a single Schneider XW system, 
> or possibly a Radian. 
> I would like to give him the ability to switch from the Fronius inverter to a 
> 600V charge controller if either a) the grid went down or b) the Fronius 
> failed. 
> 
> I looked at Morningstar's TS-MPPT-600 controller with the DC transfer switch, 
> but its DC output is rated as limited to 60A, less than the 4.2kW output of 
> the array. The spec sheet gives a nominal maximum wattage of 3,200W, although 
> a note adds that "input power can exceed Nominal Maximum Operating Power, but 
> controller will limit and provide its rated continuous maximum output current 
> into batteries. This will not harm the controller." 
> 
> I looked at Schneider's XW MPPT80 controller, which has the necessary higher 
> capacity. But beside lacking any built-in or optional input metering, it 
> lacks the transfer switch available with the Morningstar.
> 
> So questions:
> - Is there a good transfer switch to use with the Schneider unit, to allow 
> manual switching of the PV input between the Fronius (when the grid is up) 
> and the controller and batteries (when the grid is down)?
> - Should I use the Morningstar unit, recommending that the periodic 
> flatlining due to the excess wattage be simply accepted as a small concession 
> to being able to use the array during an extended outage?
> - Is AC coupling simply a better approach?
> - Any other solutions?
> 
> Thanks, Allan
> 
> -- 
> Allan Sindelar
>  <mailto:al...@sindelarsolar.com>al...@sindelarsolar.com 
> <mailto:al...@sindelarsolar.com>
> NABCEP Certified PV Installation Professional
> NABCEP Certified Technical Sales Professional
> New Mexico EE98J Journeyman Electrician
> Founder (Retired), Positive Energy, Inc.
> 505 780-2738 cell
> 
>  
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org 
> <mailto:RE-wrenches@lists.re-wrenches.org>
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
> <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
> 
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to