Hi Wrenches,
 
I know I have seen this somewhere before but can't seem to locate it in the 
archives. Recently and AHJ rejected our plans because, although we were 
compliant with the 120% rule applied to the busbar on the existing sub which 
was our solar PCC, the existing breaker feeding the existing sub (our PCC) 
exceeded the 120% as it applied to the bus in the main. I was under the 
impression that the 120% applies to the bus at the PCC and that existing 
equipment "downstream" or "upstream" of the PCC need not be retrofitted to 
comply with the 120% rule (conductor ampacity aside).
 