When the generator is auto started, the inverter's charger will be
enabled. After the generator is stopped, the inverter's charger will be
returned to the mode before the generator started. The logic is if you
are running the generator the Inverter's charger should be enabled. You
could lower the charger AC limit to 0 Amps.
08:00 Inverter charger OFF
10:00 Must run start -> charger ON
11:00 Must run stop -> charger OFF
>Darren
On 04/27/2016 05:31 PM, jay wrote:
HI All,
I’ve got a problem that outback tech hasn’t been able to figure out.
off grid system
mate 3
quad stacked VFX 3648
The generator is set to specific start/stop daily timer. This works fine.
The client has plenty of solar for the day, and when he runs his generator he
doesn’t want the chargers to operate.
OK so just hit charge off, and yes the chargers will turn off.
But next day, genny starts up, and the chargers come back on as well.
Outback says that shouldn’t be happening, but it is.
Anybody have this issue or know of a fix?
Thanks
jay
peltz power
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org