When the generator is auto started, the inverter's charger will be enabled. After the generator is stopped, the inverter's charger will be returned to the mode before the generator started. The logic is if you are running the generator the Inverter's charger should be enabled. You could lower the charger AC limit to 0 Amps.

08:00 Inverter charger OFF
10:00 Must run start -> charger ON
11:00 Must run stop -> charger OFF

>Darren


On 04/27/2016 05:31 PM, jay wrote:
HI All,

I’ve got a problem that outback tech hasn’t been able to figure out.

off grid system
mate 3
quad stacked VFX 3648

The generator is set to specific start/stop daily timer.  This works fine.

The client has plenty of solar for the day, and when he runs his generator he 
doesn’t want the chargers to operate.
OK so just hit charge off, and yes the chargers will turn off.

But next day, genny starts up, and the chargers come back on as well.

Outback says that shouldn’t be happening, but it is.

Anybody have this issue or know of a fix?

Thanks

jay

peltz power


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to