Larry,
When you say "customers ruin the batteries" are they
sulphating to death or electrolyte getting too low or? And your sure
its due to the lack of...cycling? watering? proper charging? during the
prolonged periods or just poor care overall.
Thanks for a bit more insight.
Bill
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
On 5/1/2016 9:54 AM, Starlight Solar Power Systems wrote:
Seasonal use is a very frequent application that we design for in
Mexico and Canada. Usually the seasonal residence sets for 6 months or
longer. We have tried several methods of preserving flooded battery
life including water-miser caps, short absorb times, no absorb time, 2
stage charge with the CV below gassing point and battery additives.
Even so, more than half of our Mexico customers ruin batteries in 3-5
years due to prolonged periods without maintenance. The northern
customers fair much better.
AGM’s perform much better than flooded but Lithium batteries are the
best for long term non-use. You can simply discharge the battery to
50% then turn off the battery and walk away. When you return in 6-7
months, you will find it at the same SoC as when you left. For long
term seasonal storage, that is all I recommend anymore.
Larry Crutcher
Starlight Solar Power Systems
On Apr 30, 2016, at 12:54 PM, Dana <d...@solarwork.com
<mailto:d...@solarwork.com>> wrote:
I have yet to see any FLA battery that can go 4-5 months without
service. Typically a FLA needs an increased voltage to attain the same
full charge rating at low temps, but you still require watering. I
have clients with shut down houses and no load situations, we back off
the Absorb set point voltage, & time at full & they still require
watering.
This thread started with “? I don't think the friend will be savvy
enough to disconnect/connect them every year and I don't feel like
having to go out there every season for them.”
Based on this statement would you still recommend FAL batteries? I
have clients with AGMS that are partial year residents & their AGMS
are at 8-10 years and still doing the job. That said some clients even
full time occupants cannot water & test the SG on a FLA to save their
life (or sustain the batteries life).
----------------------------------------------------------------------------
Dana Orzel
Great Solar Works, Inc - NABCEP # 051112-136
E - *d...@solarwork.com <mailto:d...@solarwork.com>* - Web -
solarwork.com <http://solarwork.com>
O - 970.626.5253 C - *208.721.7003*
"Responsible Technologies for Responsible People since 1988"
*P*Please consider the environment before printing this email.
*From:*RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org]
*On Behalf Of *Starlight Solar Power Systems
*Sent:* Saturday, April 30, 2016 1:28 PM
*To:* RE-wrenches
*Subject:* Re: [RE-wrenches] Winter Battery Maintenance
I agree with Todd and Bob, leave the PV solar on, EQ off.
I also instruct my customers to reduce the absorb timer to 0.1 hours.
Since the battery is staying full, there is no need to spend time
above cell gassing point which will increase water loss.
Larry
On Apr 30, 2016, at 10:28 AM, RE Ellison <reelli...@gmail.com
<mailto:reelli...@gmail.com>> wrote:
Everything mentioned so far works well however, if you're using a
charge controller with an auto equalize function.
Turn it off!
I had a friend who has left his system over the winter for years with
no issues and he shut his inverters off one year got back to the
batteries being boiled dry
After a lot of looking I figured out that it had gone into auto
equalize and since the available sunshine per day was so low that it
just kept trying all winter long to equalize the batteries
There was a battery replacement in his future relatively quickly!
It was an expensive lesson and I have since gone to all of the systems
similar to that that I have installed over the years and shut off the
auto equalize
It's not an issue if somebody's around but they were gone for like
five months and it was not a good outcome
This particular system had three charge controllers,
A combination of MX 60 and FM 60s I believe
Just my thoughts,
Bob ellison
On Apr 30, 2016, at 12:43 PM, toddc...@finestplanet.com
<mailto:toddc...@finestplanet.com> wrote:
i built a system for a friend's seasonal (summer) off-grid residence
in alaska.
my instructions were simple:
leave the pv input & cc output breakers "on" and the load breakers
(inverter, dc sunfrost etc) "off".
there was never a problem with winter freezing (even at -40f) until
one year when he accidently left the inverter's breaker on. even with
no load, the inverter's idle current drained the batteries and they
froze. he only made that mistake once.
todd
On Saturday, April 30, 2016 8:13am, "Solar" <dahlso...@gmail.com
<mailto:dahlso...@gmail.com>> said:
> I do systems like this every year. (-45F winter temps). Use quick connects and
> train the customer on the batteries and their maintenance. Find
bats with freeze
> points that match your area. I typically mount the modules at
90degree so snow
> never covers the array/module.
>
> I always recommend removal. I've thought about temp controlled
incandescent lamp
> with a timer in a battery box for really cold nights.... Haven't
got around to
> working through that design.
>
> I'm interested in the real seasoned off-grid installers thoughts
about this.
>
> Jesse Dahl
>
> NABCEP PV Installation Professional
> IBEW Local 292 - Electrician
> Electrical/Solar PV Instructor - HCC
>
> Sent from my iPhone
>
> > On Apr 30, 2016, at 9:07 AM, AE Solar
<autonomousenerg...@gmail.com <mailto:autonomousenerg...@gmail.com>>
> wrote:
> >
> > Hey Wrenchers,
> >
> > A friend wants a very small battery set up at hunting cabin (like
under 1kW).
> It will only be used in the warmer months. I'm wondering what you
all recommend
> for the batteries over the winter. I assume the ideal situation
would be that they
> would be disconnected and brought somewhere warm for the winter
(the cabin will be
> subject to below freezing temps)??
> >
> > So long as they go into the colder months with a full charge is
it alright to
> leave them hooked up? I don't think the friend will be savvy enough to
> disconnect/connect them every year and I don't feel like having to
go out there
> every season for them.
> >
> > Thanks for any thoughts.
> > Adam
> >
> > Adam Katzman
> > Autonomous Energies
> >
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
<mailto:RE-wrenches@lists.re-wrenches.org>
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
www.frenergy.net
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org