HI Scot,

I”ve pretty cavalier on lots of things.  But for this, I would use conduit and 
wire.  
I just think the added protection, being able to pull out wire in case etc.  

I do like the armored cable that was discussed, but that stuff is expensive and 
the ends are quite expensive.  

I buy my cable from Bryan at PV cables, you might give him a call for pricing.

Jay

peltz power


> On May 17, 2016, at 3:52 PM, Howard Arey <scot.a...@solarcentex.com> wrote:
> 
> Good day, wrenches.
>  
> I am installing four dual axis trackers totaling 52KW (13KW per) to four 
> individual Fronius Primo 12.5 Primo’s.  We’ve done this setup before except 
> this time, we’ll mount the inverter at the meter instead of carrying 
> inverting at the tracker and carrying 240 volt over a 300+ foot ground run 
> for the four combined trackers. And to the heart of this question, we’ll run 
> under 1,000 volt rules for this commercial ranch setup. Goal is to user 
> higher voltages and minimize amps running through conductors.
>  
> So my project is:
>  
> 4 each 13KW trackers
> Each tracker is 3 strings of 14 modules and about 705Voc and 520 Vmp. This 
> combined 3-string output for each tracker will have Isc of 8.89 x 3 = apc 27 
> amps
> We’ll pull each set of tracker conductors (4 trackers, plus one more run for 
> a 5th tracker) so 10 +/- conductors. I’ve done the necessary conditions of 
> use derates.
>  
> The big question is what would you select as this 1,000 volt rated wire for 
> conduit covered installation? PV Wire will get mighty expensive and I don’t 
> even know if I’ll find in 4AWG.
>  
> I ran into this one time before and we just did multiple strings to keep in 
> the 600volt category but I don’t want to do here because that means I double 
> the number of conductors (and go from 3200 to 6400 feet of wire…String math 
> and MPP ranges keep me at strings of 14.
>  
> I want to centrally mount the inverters instead of one at each tracker for 
> looks and reduce 240 wire sizing.
>  
> What type cable would you use?
>  
> Howard “Scot” Arey
> Owner, Solar CenTex
> 254-300-1228
> scot.a...@solarcentex.com <mailto:scot.a...@solarcentex.com>
>  
> www.solarcentex.com <http://www.solarcentex.com/>
> https://www.facebook.com/SolarCentex <https://www.facebook.com/SolarCentex>
> http://www.solarreviews.com/installers/solar-centex-reviews/ 
> <http://www.solarreviews.com/installers/solar-centex-reviews/>
>  
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to