Tell your client that the Outback Radian is an "inverter/charger" and the only things that need to programmed for charging via generator or grid are bulk, absorb, float and equalize. Nothing needs to be set on automatic. Adding an external charger would be a waste of money. How about telling them "Whenever the generator is running, it powers your big load and still uses all extra energy to charge the battery bank?"
Dan Fink Adjunct Professor of Solar Energy Technology, Ecotech Institute IREC Certified Instructor™ for: ~ PV Installation Professional ~ Small Wind Installer Executive Director, Buckville Energy NABCEP Registered Continuing Education Providers™ 970.672.4342 On Fri, Jun 10, 2016 at 8:56 AM, Howie Michaelson <ho...@suncatchervt.com> wrote: > Gary, > Is this an off-grid system? In any case, there is no reason that > connecting the generator through the Radian means the batteries will charge > automatically. And to not use the native charging capabilities of the > Radian doesn't make much sense financially or functionally. Any other > charger will either not charge the bank very well or will add substantial > cost and control issues. > > Howie > > *Howie Michaelson* > *NABCEP Certified Solar PV Installer™* > Sun Catcher, LLC > Renewable Energy Systems Sales and Service > VT Solar Electric Incentive Partner > 802-272-0004 > > On Fri, Jun 10, 2016 at 10:50 AM, gary easton <g...@arp-solar.com> wrote: > >> I have a customer that has an 8 kW outback radian system with a 516amphr >> 48 volt battery bank. He also has a large generator to power some large >> loads. He does not want the generator tied to the outback. He >> does not like automatic features but would like to run a simple battery >> charger whenever he has the generator running. Is this an issue with the >> outback system? And if not does anyone have a charger they recommend in >> this application? >> >> -- >> Sent from Gmail Mobile >> >> _______________________________________________ >> List sponsored by Redwood Alliance >> >> List Address: RE-wrenches@lists.re-wrenches.org >> >> Change listserver email address & settings: >> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org >> >> List-Archive: >> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html >> >> List rules & etiquette: >> www.re-wrenches.org/etiquette.htm >> >> Check out or update participant bios: >> www.members.re-wrenches.org >> >> >> > > _______________________________________________ > List sponsored by Redwood Alliance > > List Address: RE-wrenches@lists.re-wrenches.org > > Change listserver email address & settings: > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org > > List-Archive: > http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html > > List rules & etiquette: > www.re-wrenches.org/etiquette.htm > > Check out or update participant bios: > www.members.re-wrenches.org > > >
_______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org