Dan

Does it have System Control Panel (SCP)? If not, it's a must.

It's like having an Outback inverter with no Mate or a big LCD TV with no 
remote. 

Thank you,

Maverick


Maverick Brown

Maverick Solar Enterprises, Inc.
SunFlow Systems
Office:     512-919-4493
Cell:        512-460-9825

Sent from an iPhone. 

> On Jul 18, 2016, at 7:57 PM, Dan Fink <danbo...@gmail.com> wrote:
> 
> Thanks you for your help. I'm a poor off-grid guy. This should be a learning 
> experience then....the one time I visited the system around 10:AM,, both CCs 
> were in Bulk, and no grid blackout the night before.
> Methinks I should also borrow a programming dongle from a colleague for this 
> one....
> 
> Dan Fink
> Adjunct Professor of Solar Energy Technology, Ecotech Institute
> IREC Certified Instructor™ for: 
> ~ PV Installation Professional
> ~ Small Wind Installer
> Executive Director, Buckville Energy
> NABCEP Registered Continuing Education Providers™
> 970.672.4342
> 
>  
> 
>> On Mon, Jul 18, 2016 at 6:27 PM, Maverick Brown <maver...@mavericksolar.com> 
>> wrote:
>> Dan
>> 
>> Barring some non-factory-default settings, they are not likely running on 
>> battery power at night. 
>> 
>> When the grid is up, the inverter will go silent at night (asleep) [with --- 
>> three dashes on its LED display]. That's good. 
>> 
>> During the day, the inverter will "prevent" the battery voltage from going 
>> above its sell voltage (unless some other mode is on like Grid Support or 
>> Standby, etc.) The charge controllers will attempt to Absorb & Float, but 
>> the inverter will offload the energy by keeping the voltage at the Sell 
>> setting. I generally set Sell to the recommended Float Voltage++. I set the 
>> charge controller float to 1.0v higher and Absorb as appropriate. 
>> 
>> There is a lot more to unpack here. 
>> 
>> Flooded batteries will consume a good amount of power just to maintain 
>> float. 
>> 
>> As a defense against sulphated plates forming, I program the inverter EQ 
>> button for a heavy Absorb / mild EQ and instruct the customer to press it 
>> (every other month opposite month from watering??)
>> 
>> Are you getting 20-25 kWh per day in production?
>> 
>> PS having the inverter always feed the critical loads panel is exactly it's 
>> intended use. 
>> 
>> Thank you,
>> 
>> Maverick
>> 
>> 
>> Maverick Brown
>> 
>> Maverick Solar Enterprises, Inc.
>> SunFlow Systems
>> Office:     512-919-4493
>> Cell:        512-460-9825
>> 
>> Sent from an iPhone. 
>> 
>>> On Jul 18, 2016, at 6:50 PM, Dan Fink <danbo...@gmail.com> wrote:
>>> 
>>> Maverick; it's 6.0 kW of PV, 2 Midnite Classic 200s, Conext XW+ 5548, and 8 
>>> Crown Embassy VRSLA 6CEA390 for 390 amp-hours, 48v. Concerns me to be 
>>> cycling those batteries every night when it's not supposed to happen as per 
>>> the permit package.
>>> "Notes - Battery Backup: During an outage, an automatic transfer switch in 
>>> the inverter opens the grid interconnect, isolating the inverter from the 
>>> utility to prevent back-feeding the local power lines. The inverter then 
>>> draws from the battery bank to provide AC power to the backup sub-panel. 
>>> Battery power is only used to provide power to the backup sub-panel. The 
>>> Battery inverter only sells energy to the grid from the solar array when 
>>> available and not from the battery bank. The battery backup inverter is UL 
>>> 1741 and IEEE 1547 compliant."
>>> 
>>> Dan Fink
>>> Adjunct Professor of Solar Energy Technology, Ecotech Institute
>>> IREC Certified Instructor™ for: 
>>> ~ PV Installation Professional
>>> ~ Small Wind Installer
>>> Executive Director, Buckville Energy
>>> NABCEP Registered Continuing Education Providers™
>>> 970.672.4342
>>> 
>>>  
>>> 
>>>> On Mon, Jul 18, 2016 at 5:23 PM, Maverick Brown 
>>>> <maver...@mavericksolar.com> wrote:
>>>> Dan
>>>> 
>>>> Does the inverter go silent at night? (---) on the inverter display?
>>>> 
>>>> There are lots of settings that can influence sell amount. 
>>>> 
>>>> What type and size is the battery bank? 
>>>> 
>>>> What is the solar size?
>>>> 
>>>> Thank you,
>>>> 
>>>> Maverick
>>>> Cell:        512-460-9825
>>>> 
>>>> Sent from an iPhone. 
>>>> 
>>>>> On Jul 18, 2016, at 5:56 PM, Dan Fink <danbo...@gmail.com> wrote:
>>>>> 
>>>>> Installer went out of business, all I have to troubleshoot with is an 
>>>>> as-built 3-line that "may or may not be right." The charge controllers 
>>>>> are a pair Midnite Classic 200s. Customer complained that system selling 
>>>>> only 2/3 of what was predicted back to the utility; that appears to be 
>>>>> because everything out of his critical loads subpanel is running off the 
>>>>> battery bank all night, every night, grid or no, so it takes 1/3 of the 
>>>>> day to get the batteries charged up again every day and start selling to 
>>>>> the grid.
>>>>> 
>>>>> I have very little experience with the XW+ thus my question for the folks 
>>>>> here. My plan for next week is to show up, make my own as-built 3-line, 
>>>>> and recommission the inverter. Anyone else seen this sort of thing 
>>>>> before? Hard to believe that an electrician would mis-wire or not wire 
>>>>> the bypass, I'm thinking software setting.
>>>>> 
>>>>> 
>>>>> Dan Fink
>>>>> Adjunct Professor of Solar Energy Technology, Ecotech Institute
>>>>> IREC Certified Instructor™ for: 
>>>>> ~ PV Installation Professional
>>>>> ~ Small Wind Installer
>>>>> Executive Director, Buckville Energy
>>>>> NABCEP Registered Continuing Education Providers™
>>>>> 970.672.4342
>>>>> 
>>>>>  
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List-Archive: 
>>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>>> 
>>>>> List rules & etiquette:
>>>>> www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> www.members.re-wrenches.org
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> List Address: RE-wrenches@lists.re-wrenches.org
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> List-Archive: 
>>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>> 
>>>> List rules & etiquette:
>>>> www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> www.members.re-wrenches.org
>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> List Address: RE-wrenches@lists.re-wrenches.org
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> List-Archive: 
>>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>> 
>>> List rules & etiquette:
>>> www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> www.members.re-wrenches.org
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings: