Wrenches
We have done transformers for issues just like this with good results, the cost
vs the new wire, conduit and trenching must be done to make sure which
direction. We have had to use paired mcm 300 to make residentual so run the
numbers
Jerry
Sent via the Samsung Galaxy S™ III, an AT&T 4G LTE smartphone
<div>-------- Original message --------</div><div>From: Chris Schaefer
<ch...@solarandwindfx.com> </div><div>Date:08/16/2016 7:53 AM (GMT-10:00)
</div><div>To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
</div><div>Subject: Re: [RE-wrenches] Buck-Boost transformer to mitigate high
voltage drop? </div><div>
</div>Perhaps I missed it but you didn't say what you measured the voltage to
be at the clients service entrance panel at his house?
Christopher
On Tue, Aug 16, 2016 at 1:40 PM, Mac Lewis <maclew...@gmail.com> wrote:
Yes, what current did you use to calculate that voltage drop? How big is the PV
system?
On Aug 16, 2016 11:38 AM, "Chris Mason" <cometenergysyst...@gmail.com> wrote:
How much of the power produced will be self-consumed, how much will be exported?
On Tue, Aug 16, 2016 at 12:16 PM, Howard Arey <scot.a...@solarcentex.com> wrote:
Good day,
I have a potential client that has an existing 1,000 foot run from the meter
and transformer at the street to the home. This is 4/0 Al and quick calcs show
the voltage drop at over 12%. He acknowledges that the wire is undersized to
keep voltage at/about 240 volts (I have not measured directly at the street /
transformer yet).
I know the wire has the necessary ampacity to carry his current service needs
and to carry amps from the to-be-suggested solar system.
My concern is that the voltage drop will change the 240 volts at the
street/transformer/meter to 211ish (or will I see a higher 268’sh voltage at
the far house end?) at the house. The inverter will try to synch to this
voltage but of course this is outside of typical inverter parameters.
So, instead of re-running much large wire, does anybody have experience and
comments about potentially using a buck-boots transformer at the home to get us
back to 240 volts? This would need to be service entrance sized.
Howard “Scot” Arey
Owner, Solar CenTex
254-300-1228
scot.a...@solarcentex.com
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Chris Mason
NABCEP Certified Solar PV Installer™
Solar Design Engineer
Generac Generators Industrial technician
www.cometsolar.com
264.235.5670
869.662.5670
Skype: netconcepts
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
--
Chris Schaefer’s
Tel/Fax 585-229-2083 or Cell 585-748-1870
5115 South Hill Road ~ Canandaigua New York 14424
www.solarandwindfx.com ~ E-mail: ch...@solarandwindfx.com
Thomas Jefferson, the author of our great Constitution, once said, "democracy"
will cease to exist when you take away from those who are willing to work and
give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org