I got zapped on a neutral in a generac transfer switch that I thought was
de-energized.  Someone prior had moved hots from the transfer switch to the
main panel, but not the neutrals.  I was disassembling connections in the
transfer switch as part of a move to a battery-backup system and I could
not believe it when I got popped.  The experience drove home the importance
of terminating the phase and neutral in the same enclosure.

On Thu, Sep 8, 2016 at 8:22 PM, Chris Mason <cometenergysyst...@gmail.com>
wrote:

> You have to splice the load cabling in the main panel, otherwise you would
> need to run new conduits and cables. There's nothing that I know of that
> prevents you splicing wires.
> I disagree with the response that you do not need to move the neutrals.
> You should never have the load's phase wiring in one panel and the neutral
> in another.
>
> On Thu, Sep 8, 2016 at 8:00 PM, Mac Lewis <maclew...@gmail.com> wrote:
>
>> Hello wrenches,
>>
>> We run into many scenarios where we are locating a critical load panel
>> adjacent to an existing service to make it easy to move the loads.  I've
>> always taken it for granted (as have the electricians that we use) that we
>> can't do a splice in the main panel and extend the load wiring to the
>> critical load panel.  Is there code violation for doing a splice in the
>> main panel and extending the leads to the critical panel?  You would be
>> treating the service panel as a pass-trough/splice box for those critical
>> loads.
>>
>> It makes me wonder because of all of the prewired transfer switch
>> packages with wire whips already attached that seem to be designed to do
>> just that.
>>
>> Code references would be appreciated.
>>
>> Thanks
>>
>> --
>>
>>
>>
>> Mac Lewis
>>
>> *"Yo solo sé que no sé nada." -Sócrates*
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches@lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenc...@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
Matt Sherald
PIMBY Energy, LLC
NABCEP Certified Solar PV Installer®
304-704-5943

www.getpimby.blogspot.com
www.getpimby.com
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to