Brad, which has been discontinued, the SMA 240’s or Trimetric? While we don’t 
have a large collection of Enphase systems, after they are installed when 
needed to think of them at all, we have a consensus among owners of 
satisfaction especially in terms of monitoring and troubleshooting that goes 
with microinverters. 

 

I’m learning new features on Enphase’s website constantly. For what string 
inverter can you see a continuous graph of DC volts and input current, AC 
output volts and current, as well as frequency and internal temp of the 
inverters at the module level? At this point we may have slightly over 1% 
failure rate on systems that are up to six years in the field. Keep in mind 
that while there is talk of capacitors failing, SMA 240’s also uses a row of 
paralleled caps.

 

And I sense an uptick in installer support.

 

There is one area where string inverters have an advantage and that is the 
ability to place a lightening arrester between the module(s) and the inverter, 
making micros more vulnerable in that regard.

 

Bill Dorsett

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Bradley Bassett
Sent: Thursday, September 15, 2016 10:02 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] micro-inverters

 

My SMA micro-inverters have been rock solid for a couple of years. They do not 
taper off and do not communicate with the Sunny Island. The only issue I've had 
is that it seems that an internet connection is needed for the monitoring to 
work, even for the local monitoring. If there is no monitoring ie: power outage 
for the neighborhood DSL, then there is no direct way to see if they are 
working or not. Indirectly when off grid, my Trimetric is the best source of 
information on charge or discharge. A separate kWh would of course provide more 
accurate info on their status.

I believe that these have been discontinued now though.

 

Brad

AEE Solar

 

On Thu, Sep 15, 2016 at 6:46 AM, Drake <drake.chamber...@redwoodalliance.org> 
wrote:

Is it the consensus that Enphase 215 inverters on are the most reliable micro 
inverters (even though the tech support may be lacking these days)? 

Someone on this list mentioned that the SMA micros had a rocky time of it. What 
were the problems with these? 

Do the SMA micro inverters taper charge when AC coupled with Sunny Islands?

Drake Chamberlin
Athens Electric LLC
OH License 44810
CO License 3773
NABCEP Certified Solar PV 
740-448-7328
http://athens-electric.com/ 

At 03:24 PM 9/14/2016, you wrote:




Re 190's.

Not much to learn from dissecting a swollen 190. Most of the time the swelling 
is caused by electrolytic capacitors that have failed. Some very high current 
capacitors actually have brackets to bolt them down to minimize swelling.

Frank BZP.

BZ Products INC.
8801 Gravois Rd.
St.Louis MO 63123 USA
314-644-2490
www.bz-products.net

On 9/14/2016 1:58 PM, Benn Kilburn wrote:



You guys should really cut one of those swelled up ones and share the photos 
with us :)

Benn Kilburn 
SkyFire Energy Inc. 
780-906-7807

On Sep 14, 2016, at 11:14 AM, Jerry Shafer <jerrysgarag...@gmail.com > wrote:




The 190's had component issues which case them to balloon up
Jerry

On Sep 14, 2016 10:11 AM, "William Miller" <will...@millersolar.com > wrote:

Colleagues:

We have M190s fail in beach installations. Some have had the cases swell up 
like there is a tumor inside. I haven't cut them open to see what's inside 
because they need to go back to manufacturer. 

William

On Sep 14, 2016, at 9:32 AM, Jerry Shafer <jerrysgarag...@gmail.com > wrote:




Mike

I also work near the ocean, its all around me here in Hawaii, we have had the 
190's fail but not to environmental conditions and very few issues with 215's. 
Do you have any pics of the damage as l have seen very little salt issues.

Jerry

On Sep 13, 2016 9:11 PM, "Mike Nelson" < mdelectricso...@gmail.com 
<mailto:mdelectricso...@gmail.com> > wrote:

I've had so many Enphase failures it's kind of ridiculous. We install most of 
our systems near the ocean so corrosion has played a big factor. The newer 
micro inverters are holding a much better, 215 and 250's. I have learned over 
the years that SMA makes the best product, and I mostly stick with them. 
Sometimes micro inverters are requested or really fit the installation 
particulars, so I still use them occasionally. I haven't yet tried solar edge.

Michael D Nelson

MD Electric & Solar, Inc.

707-684-0064 mobile

707-884-1862 office

www.mdelectricsolar.com 

Sent from my iPhone

On Sep 13, 2016, at 6:23 PM, Rebecca Lundberg < rebecca.lundb...@gmail.com 
<mailto:rebecca.lundb...@gmail.com> > wrote:




Esteemed wrenches,

I'm hoping the experience of this list can help give us a broader perspective 
on the current market performance and as a secondary concern, tech support (or 
lack thereof), from solar micro-inverter manufacturers.

Are others having much trouble with micro-inverters? We have had repeated 
issues with several different brands on our systems in Minnesota:

- 8 Enphase systems with mostly M210 and M215, have had to repeatedly go back 
to sites to replace units. The new replacement ones seem to be lasting better 
(we sure hope they will). Enphase is harder to contact in recent years, but 
we're happy they at least provide a predictable stipend. Are you also having to 
replace a lot of this brand of product? Are the newer models holding up better?

- We gave a new inverter busbar design concept a try (tenKsolar) and though the 
micro-inverters were supposed to take turns and be 'redundant,' the ones with 
APS micro-inverters needed 100% replacement and the ones with Lead Solar 
micro-inverters have a problem where if one of them fails it appears to send a 
signal to all the rest so the entire busbar stops working -- in action it's far 
from redundant. When we purchased the tenKsolar Rais Inverter Bus (RIB) the 
spec sheet didn't tell us what brand of micro-inverter they would use as the 
OEM so we couldn't research the viability of the product or company or warranty 
stipend (or lack there-of) of the micro-inverter OEM. We assumed it was a 
tenKsolar product and they would provide warranty replacements, service, and 
tech support, but our experience has been far from that. When something goes 
wrong tenK says 'it's not our product that's failing' because they don't 
actually manufacture the micro-inverter (it's an OEM), the micro-inverter 
company says 'it's not our product' because tenKsolar has it wired and used in 
a very unique manner specific to the tenKsolar product, so both manufacturers 
are backing away from any responsibility. A 25-year warranty on the inverter 
busbar is a great concept but if/when something goes wrong there is no support 
and no apparent warranty at all except maybe they will send us a new component 
that needs several hours of work to re-install, so either the installer does 
the warranty work for free or the customer has a very unexpected expense to get 
their system back up and running a year or two after it was installed; we think 
both scenarios are unacceptable (from our installer perspective :-), do any of 
you have experiences you can share here?

I'm wondering if the climate in MN makes us an anomaly. Based on these 
micro-inverter experiences we feel like the Rapid Shutdown rule has forced us 
to use dc optimizers on residential applications whether we want to or not -- 
is that pretty much what all of you are doing too? 

Rebecca Lundberg

_______________________________________________

List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

Check out or update participant bios:

www.members.re-wrenches.org

 

_______________________________________________

List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

Check out or update participant bios:

www.members.re-wrenches.org



_______________________________________________

List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

Check out or update participant bios:

www.members.re-wrenches.org

 

_______________________________________________

List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:

http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 

List rules & etiquette:

www.re-wrenches.org/etiquette.htm

Check out or update participant bios:

www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org





_______________________________________________
List sponsored by Redwood Alliance
 
List Address:
 <mailto:RE-wrenches@lists.re-wrenches.org> 
RE-wrenches@lists.re-wrenches.org
 
Change listserver email address & settings:
 <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org> 
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive:
 <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html> 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
 <http://www.re-wrenches.org/etiquette.htm> 
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
 <http://www.members.re-wrenches.org> 
www.members.re-wrenches.org
 





  _____  

 <https://www.avast.com/antivirus> Avast logo <https://www.avast.com/antivirus> 
 

This email has been checked for viruses by Avast antivirus software. 
www.avast.com <https://www.avast.com/antivirus>  

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/>  

  _____  


 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
 Avast logo

This email has been checked for viruses by Avast antivirus software. 
www.avast.com 
<https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
  

 


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to