Electrical noise coming in from the utility side
can also cause an arc fault code.

At 07:32 AM 11/11/2016, you wrote:
This array is a ground mount, so not on a roof, and no radio towers nearby.

As for grounding, The array and the shed with
the interconnection point are in the same area.
There are a couple ground rods there, which
everything on the AC side is connected to,Â
including a #6 wire from each inverter. there is
just a #10 ground coming from the array to the inverters.Â
The house is a couple hundred feet away and has
its own grounding electrode system.

Jerry,
The inverters are new (replaced 2 months ago),
but it is a good idea to check firmware.
As for AC loads, nothing stands out as the types
of things you mentioned, although there
may be a well pump. They also do have a large
water storage tank for heating, but they
say that they have not needed to use it yet this
year. Then there is also the generator...

Thanks for your recommendations.
-Dave



--

Dave Tedeyan
Project Engineer

Taitem Engineering, PC
109Â S. Albany Street, Ithaca, NY 14850
Voice:Â (607) 277-1118 x121
<http://www.taitem.com/>www.taitem.com

On Thu, Nov 10, 2016 at 9:51 PM, Jerry Shafer
<<mailto:jerrysgarag...@gmail.com>jerrysgarag...@gmail.com> wrote:
Dave.
We have many TL-22 in the field and they will
detect faults even when they are normal
contactor faults, have you made sure the SW is
the latest, last I checked it is 2.65.3R and it
may have a patch in there, you can turn off the
feature for testing only and see if you melt
something down but if you do please be on site
as a arc may happen. Do you have a well, AC
system with contacts, welders, compressors,
anything that has a dry contacts that brakes
under load, this is another place I would look.
Every time we have had a code out it was real
weather from something normal or a wire issue.
Not to brag but we have hundreds in the field
from the 3's to the 24's and as much as I dread
getting a call with this issue I can usually
find the problem and it can be either AC or DC.
Jerry

On Thu, Nov 10, 2016 at 8:14 AM, Dave Tedeyan
<<mailto:dtede...@taitem.com>dtede...@taitem.com> wrote:
Hi All,Â

Maybe someone will have some ideas for why a
couple inverters keep arc faulting:

-There are two SB7000TL-22 inverters, Sunpower branded.
-3 Strings of 7 SPR-327's to each inverter. Kept separate until the inverter.
-Ground mount about 50' from the shed where the
inverters are located (indoors)
-Simple grid connected system, no batteries.
-There is a whole house generator co-located in the shed.
-We interconnect by using piercing taps on the
line side of the generator transfer switch
-There has been only one power outage there
since the system was installed in April, but the generator fires up weekly.

-The arc faults have been happening on both
inverters. Sometimes only one at a time,
sometimes both will go within a day of each other.
-The events have been approximately one a month,
but sometimes more, sometimes less.

-We have already checked every single connection
in the system twice, by two different people.
-We have replaced the underground wires (and they looked just fine)
-We have replaced all home runs.
-We have replaced both inverters.
-Arc faults are still happening.
-Arc faults are not always on the same day/time of the week.

I am wondering if this can be caused by the generator?Â
Has anyone run into a situation like this or something similar?

Thanks for your help,
Dave

--

Dave Tedeyan
Project Engineer

Taitem Engineering, PC
109Â S. Albany Street, Ithaca, NY 14850
Voice:Â (607) 277-1118 x121
<http://www.taitem.com/>www.taitem.com

_______________________________________________
List sponsored by Redwood Alliance

List Address:
<mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org




_______________________________________________
List sponsored by Redwood Alliance

List Address:
<mailto:RE-wrenches@lists.re-wrenches.org>RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
<http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
<http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
<http://www.members.re-wrenches.org>www.members.re-wrenches.org



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


---
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to