Hi William, 

We have had a very similar experience with the Mate3, prior to their new 
programming guidelines that are now being shipped with the Mate3, when all we 
had was the 180 page manual. What went wrong if my memory serves here is we did 
go through the menu programming our needs for the system, then went into the 
Wizard to do a save. Not a good idea as this dumped all our programming, 
including the stacking setting, allowing the slave to parallel the Master, 
oops. Not good with the client looking on as the house goes dark and red lights 
are flashing. Luckily the back fed Master shut down without smoke coming out. 
The rest of the menu was scrambled too.

Always going to Save Config now, as the final word and programming in the 
latest revision too.

Don’t know if this helps, hope so.

 

Chris Worcester

Solar Wind Works

NABCEP Certified PV Installer

Office 530-582-4503

Cell 530-448-9692

Fax 530-582-4603

www.solarwindworks.com

ch...@solarwindworks.com

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of William Miller
Sent: Thursday, November 10, 2016 8:26 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Outback Programming Ghost

 

Ray:

 

I have no reason to believe anyone has been meddling. No one knows the 
password. It does look like some serious glitch. 

 

William


On Nov 10, 2016, at 6:25 PM, Ray Walters <r...@solarray.com> wrote:

It almost sounds like someone got in there and tried to reprogram stuff 
themselves.  Have you installed the proper anti-Gremlin devices?



R.Ray Walters
CTO, Solarray, Inc
Nabcep Certified PV Installer, 
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 11/10/2016 12:34 PM, William Miller wrote:

Colleagues: 

 

I maintain an off-grid, 8 stack FX Outback system with 3 charge controllers.  
The system has been on line for about 6 years.  It got upgraded about 7 months 
ago with 2 Mate3s.

 

About a week ago the system shutdown, leaving the customer without power.  A 
maintenance worker started a generator and power was restored.  I did not hear 
about the situation for several days.

 

A maintenance supervisor was dispatched yesterday to work with me over the 
telephone to see if we could restart the system.  The system would only run if 
the inverter output breakers were all off.  

 

I examined the system via Optics.  I was very surprised to see that the system 
programming was absolutely scrambled.  This was so much so that even the 
stacking settings were wrong.  For example, inverter 2 was set as a Master, 
which we all know will crash any system.  Other settings were also found with 
very random values.

 

This system was running prior to last Friday, so the stacking at least must 
have been right prior to the outage.  I am completely mystified as to how this 
could have happened.  

 

I am in conversation with Outback who is taking this seriously.  I have not 
heard back from them yet but I am curious if anyone else has experienced this 
or anything similar.  I'd like to broaden my knowledge on this situation to 
enhance my understanding and to share any findings with the group.

 

Thank you in advance for any input.

 

William Miller






_______________________________________________
List sponsored by Redwood Alliance
 
List Address: RE-wrenches@lists.re-wrenches.org
 
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
 
List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
 
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
 
Check out or update participant bios:
www.members.re-wrenches.org
 

 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to