Greetings Dave, Have you considered possibly installing a hybrid type transient voltage surge suppressor (TVSS), to include filters to remove high frequency EMI/RFI? Or possible a straight line filter device? If this nuisance arc fault issue is still occurring and it may be related to an AC issue you may be able to get some technical help and advice from an engineer at one of the TVSS manufacturers such as Total Protection Solutions, Richmond, VA 800.647.1911 or Surge Suppression Incorporated, Destin, FL 888.987.8877. I would also recommend reaching out for an application engineer in the SPD division at Eaton. Eaton Technical Resource Center 800.809.2772. SSI also has a very experienced field troubleshooting technician they send all around the country to help contractors with difficult electrical issues... Of course that would probably cost $1000-$2000 per day.
I avoid using piercing taps and connectors. I prefer to use service entrance tap boxes, insulated multi port connectors, or line side rated power distribution blocks. I cannot help but wonder if there may be an actual arc event occurring at one or more of the piercing taps which is somehow picked up by the DC AFCI. In commissioning this system it would be a good idea to use a non-contact IR thermometer and/or thermal imaging camera/scope to check the piercing taps for excessive heating while the conductors are energized and carrying peak currents. I hope you are successful in resolving this issue soon. I will continue to follow the thread. Hopefully we can all learn something from this. Best regards, ----MATT Matthew Sirum P.O. Box 1227 Greenfield, MA 01302-1227 USA phone: +1.413.773.0611 email: matthewsi...@gmail.com _______________________________________________ List sponsored by Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org Change listserver email address & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out or update participant bios: www.members.re-wrenches.org