When I'm evaluating an old system, one thing I do is really yank on all the battery connections. If it turns, tighten it down, and in several cases, the cable just pulls loose from the connector. They are time consuming to do right. Cable has to be stripped long enough, the crimper needs to be set correctly, and be the right crimper for the particular lug.
Below is an example of:
the wrong cable (THHN, not X Flex)
Not enough cable stripped
Wrong Size Lug
Not Crimped Properly
Not Vaselined

Now let's put 150 amps continuous through that garbage and see if we have some long term issues......

R.Ray Walters
CTO, Solarray, Inc
Licensed Master Electrician
Solar Design Engineer
303 505-8760

On 1/21/2017 3:16 PM, Dan Fink wrote:
Last weekend. 3-year old, 24v battery bank, series/parallel.
6v Trojan L-16 in an 8-battery bank, one battery on one string showing 4v. Negative end of string. Replaced the one upstream of it last summer, same problem. Aha! I say, and folks here on the Wrenches list (including me) complaining about Trojan cell failures, factory defects (I've had one too) and that the battery on the negative end fails first. Darn you Trojan. Up your game.

3yr - 3yr - 3yr - 3yr
4v - new - bubbling - 3yr

So as I am disconnecting this string so the homeowner has at least half a battery bank, I can hear the next battery upstream of the NEW one bubbling, with no power in or out, system shut down. Didn't need the thermal imager this time, we could feel it was hot.

And, as we are doing this disconnect and pulling off interconnects, the cable between the 4v battery and the new one pulled right out of the ring terminal lug. Bad crimp. Cause of problem now known. These were factory interconnects purchased from AltEDirect.com.

Never again...I have the tools to make up interconnects and do it on small projects, it's just they are so time consuming to do right (crimper, glue-melt heat shrink, etc) that it costs me more in labor (unless I have student interns working for free) than buying them from AltE.

That crappy crimp cost my customer 3 Trojan L-16s. I have notified AltE. They should be ashamed.

I believe it was Mr. Tom Duffy, SolarBiz, on this list who pointed out during the Trojan thread that cell failures were rare, most failures are due bad connections. I've had a real cell failure (Trojan J185) but in this case, Mr. Duffy was spot-on.

Best regards;



Dan Fink
Adjunct Professor of Solar Energy Technology, Ecotech Institute
IREC Certified Instructor™ for:
~ PV Installation Professional
~ Small Wind Installer
Executive Director, Buckville Energy
NABCEP Registered Continuing Education Providers™
970.672.4342 <tel:970.672.4342>


On Sat, Jan 21, 2017 at 7:54 AM, cwarfel <cwar...@entech-engineering.com <mailto:cwar...@entech-engineering.com>> wrote:

Hi David, do you have any pictures of this that could be shared? Chris


    On 1/20/2017 12:52 PM, Dave Palumbo wrote:

    Following is an entry from a Backwoods Solar email that I
    received today. I would like to share this as a teachable point
    for RE techs not familiar enough with proper battery bank care
    and as a reminder for those of us with years of storage battery
    experience.

    I have underlined the two issues in the Backwoods email copied
    below my bullet points to highlight the teachable issues.

    ·Checking wiring connections: Check not only for tightness but
    also for temperature. There are two simple methods that work
    well: #1) Use an IR Thermometer to ensure all connections are of
    a similar moderate temperature. #2)  Use your fingers to check
    temperatures. I'm practiced at this second method because
    inexpensive IR thermometers were not available when I began to
    care for storage batteries. I simply use my bare fingers (with a
    light coating of petroleum jelly) to wiggle test each battery
    cable at the battery terminal. Fingers are sensitive enough to
    gauge proper temperature. I have easily found several warm or hot
    connection points over the years caused by loose or corroded
    hardware. Do this as preventive maintenance every time you water
    the batteries or bi-monthly with sealed cells. Corrective
    measures (tightening, or taking apart and cleaning, or replacing,
    and reinstalling) are taken immediately when a warmer than usual
    connection is identified.

    ·It is not recommended by most veteran wrenches to use any
    "anti-corrosion paste" on the terminal connections. This has been
    discussed a few times over the years on the Wrenches list. Most
    of us have found that a thin coating of petroleum jelly (Vaseline
    is one brand) does the best job of protecting against corrosion
    while still allowing some visual inspection.

    from Backwoods Solar 1/20/17.  << This past summer Backwoods had
    a visit from one of our retired co-workers, xxxxx.  While it is
    always good to have friends visit, the circumstances for his
    dropping by were less than ideal.

    A small, catastrophic failure had led to the loss of a battery
    bank, two inverters, and a voltage converter. Ultimately, the
    failure was traced back to a single nut and bolt in the battery
    bank cable connections, that had developed hidden corrosion over
    time.  Corrosion causes resistance to the flow of electricity,
    which in turn generates heat.  With enough corrosion, and enough
    current flow, the amount of heat generated can be sufficient to
    melt battery terminal connections; which is exactly what happened
    in xxxxx’s case. The melted metal flowed between the negative and
    positive terminals of his industrial battery, causing a high
    power short that was beyond the capabilities of any of the
    circuit protection, resulting in the damage to the equipment.

    Now keep in mind, xxxxx is one of the more detail-oriented people
    we’ve had here at Backwoods.  The discipline of a military
    background, along with critical thinking of an engineer, were
    still not enough to overlook one very tiny detail.  xxxxx does
    his mechanical maintenance on a routine schedule; _checking for
    tightness in wiring connections_, cleaning accumulated spray off
    battery tops, cleaning out dust and spider webs, _and keeping his
    battery terminal posts coated with anti-corrosion paste._  This
    is not the type of person you’d expect to see such a failure.

    So what happened?  It all boiled down to the battery terminal
    connections.  What xxxxx had NOT done, was dissembled the nut and
    bolts from the battery terminals and cables to check for
    internal, hidden corrosion.  It had been about 6 years since he
    had done that level of inspection. When previously reviewed, the
    hardware had been thoroughly inspected, cleaned, and
    re-assembled, and then coated with _anti-corrosion paste on the
    exterior_.  In one of the 16 nut/bolt pairs, a small bit of
contamination or moisture must have been left trapped inside. Over the course of the next six years, the corrosion grew,
    contaminating the entire connection; but was NOT visible
    externally at all! >>

    Best regards,

    Dave

    David Palumbo

    Independent Power LLC

    462 Solar Way Drive

    Hyde Park, VT 05655

    802-371-8678 <tel:%28802%29%20371-8678> cell

    802-888-4917 <tel:%28802%29%20888-4917> home



    _______________________________________________
    List sponsored by Redwood Alliance

    List Address:RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org>

    Change listserver email address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>

    
List-Archive:http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>

    List rules & etiquette:
    www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm>

    Check out or update participant bios:
    www.members.re-wrenches.org <http://www.members.re-wrenches.org>

-- Christopher Warfel, PE
    Entech Engineering, Inc.
    401-466-8978 <tel:%28401%29%20466-8978>

    _______________________________________________ List sponsored by
    Redwood Alliance List Address: RE-wrenches@lists.re-wrenches.org
    <mailto:RE-wrenches@lists.re-wrenches.org> Change listserver email
    address & settings:
    http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
    <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
    List-Archive:
    http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
    
<http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
    List rules & etiquette: www.re-wrenches.org/etiquette.htm
    <http://www.re-wrenches.org/etiquette.htm> Check out or update
    participant bios: www.members.re-wrenches.org
<http://www.members.re-wrenches.org>
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to