No – I have not.

 

My strongest suspect in all of this is AC / DC conflict and insulation issues.

 

For those familiar, the DC and AC conductors run in the same space. Not too 
different than other inverters, I’d say. Fronius provides a conductor insulator 
sleeve for the AC conductors when the wires cannot be physically separated t 
othe left and right side (perhaps because of location of the array and where 
conductors enter the wire space.) WE have decided to now install those no 
matter what – can’t hurt.

 

Back to the megger testing…All of these are 600V applications and the conductor 
is rated for that. But the problems mostly (but not exclusively) occur at peak 
irradiance / middle of the day which leads me to believe the combo of high DC 
and high AC finally conflicts.

 

Perhaps time to invest in a megger tester. Next step for a professional 
installer I’d say. 

 

Thank you.

 

 

Howard “Scot” Arey

254-300-1228

 <mailto:scot.a...@solarcentex.com> scot.a...@solarcentex.com

 



 

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf 
Of Glenn Burt
Sent: Monday, May 8, 2017 3:45 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Anybody else getting 240 arc fault codes on Fronius 
installs as frequently as me???

 

Have you performed insulation resistance testing on all of your wiring?

  _____  

From: Howard Arey <mailto:scot.a...@solarcentex.com> 
Sent: ‎5/‎5/‎2017 14:17
To: 'RE-wrenches' <mailto:re-wrenches@lists.re-wrenches.org> 
Subject: [RE-wrenches] Anybody else getting 240 arc fault codes on Fronius 
installs as frequently as me???

I can’t imagine I’m the only one having this problem. Starting to suspect from 
Fronius that the problem is deeper than they let on.

 

240 faults are arc-fault detection for Fronius. 

 

We have checked every variable on our end – connectors, firmware, clean wire 
pulls. My teams are not perfect but I l know they are very good and know how 
important the clean installs are for us.

 

Most but not all of my issues are with bifacial modules. 

 

Anybody else have this issue?

 

Howard “Scot” Arey

Owner, Solar CenTex

254-300-1228

scot.a...@solarcentex.com <mailto:scot.a...@solarcentex.com> 



 

_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to