AUGUST:

The Generac EcoGen is dual-fuel capable (NG or LP), comes in 6kW and 15kW versions, is 2-wire start, can be field-configured for either 120V or 240V. It's not "portable" as it does not have wheels. It's transportable though based on its footprint and weight. Also, it was specifically designed and warranteed  for off-grid applications.

Regards,

Gary Willett PE
Icarus Engineering LLC

On 6/16/17 9:36 AM, Kevin Pegg wrote:

You could use a 2 -> 3 wire converter such as the Atkinson GSCM module that will take the 2 wire output from the SI and convert to 3-wire to control a gasoline generator such as the Honda EU7000 series, or Cummins/Onan makes a good line of gasoline generators. It may be very hard to find a gas generator that has 2 wire native remote start. That is more common with larger propane or diesel generators.

 

Kevin

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of August Goers
Sent: June-16-17 7:22 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Generator choice for Sunny Island

 

Thanks for the good feedback folks!

 

We are using a Sunny Island setup because we had access to a free Sunny Island and Sunny Boy being scrapped from another site. Otherwise I was definitely planning on going with a Outback DC coupled system.

 

I think the trick here is trying to find a portable generator that has a two-wire start option. I’m looking through the usual genny suppliers and nothing has presented itself so far. Anyway, I’ll keep looking and will check out Chris’ suggestion on the nexus controller and Generac propane unit as well.

 

FYI, here is a link to what the portal is like. It’s going in National Park land by the Golden Gate Bridge so I hope we can pull it together! http://www.sharedstudios.com/

 

August

Luminalt

 

 

From: RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Chris Mason
Sent: Friday, June 16, 2017 4:56 AM
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Subject: Re: [RE-wrenches] Generator choice for Sunny Island

 

To my limited mind, the whole 120V sunny island setup is a disaster. Why not install a DC coupled 8KW Outback Radian and solve all your problems. USe any 240V generator, although finding a 2 wire start gasoline unit may be hard. I would use a Nexus controller generac propane generator with propane tank, all mounted on the container. I would never design anything to use gasoline, it's too dangerous.

 

On Fri, Jun 16, 2017 at 7:19 AM, Matthew Sirum <matthewsi...@gmail.com> wrote:

Greetings August,

Great thoughts and comments from Brian!  I would also suggest speaking
with the generator manufacturers' tech/engineering folks regarding the
120VAC configuration and to confirm 2-wire start set up once you have
a brand and model or two in mind.  Generator parts and service
availability in the region of the project may also drive brand
selection.  If you need to maximize the inverter's battery charging
capabilities (depending on battery system charging requirements) you
may end up needing to look at generators in the 7.5 kW to 8.0 kW
capacity range to allow for headroom in generator output loading.

Also; I am curious how you arrived at an AC coupled design for this
project.  I do not know any of the details or specific projects goals
you are working with, but I would potentially consider a DC coupled
system design...  DC/DC charge controller(s) would keep the battery
system charged (and any DC loads operable) even if the Sunny Island
and/or Sunny Boy(s) have a failure or is taken offline.  If most of
the AC loads are 120VAC I would consider keeping the inverter AC
output circuit 120VAC and install a dedicated transformer solely for
the 240VAC load....  Or perhaps consider a 120/240VAC inverter model.
Depending on the overall situation a DC coupled system could be more
resilient.  The dedicated transformer for the 240VAC load could also
potentially help make the system more robust.  Also; I have spoken
with a number of folks who have told me they wish the Sunny Island had
more/better features for generator integration.  I'd like to hear more
from those who have plenty of experience designing and installing
systems with Sunny Islands and generators to learn what the current
thoughts and issues are.

I hope some of these thoughts may be helpful.

Best regards,

----MATT

Matthew Sirum
P.O. Box 1227
Greenfield, MA 01302-1227  USA
phone: +1.413.773.0611
email: matthewsi...@gmail.com


--------  Original Message Below --------

[RE-wrenches] Generator choice for Sunny Island
August Goers august at luminalt.com
Thu Jun 15 09:02:41 PDT 2017

Hi Wrenches, especially those of you who work on off-grid projects,

We have an upcoming off-grid project where we will be powering a storage
container with electronics in it. The loads are mostly 120 volt but there
is a 240 volt heat pump that might occasionally run. We’re AC coupling the
Sunny Island with a Sunny Boy PV inverter. So, we’ll be installing a
Outback PSX-240 autoformer to bump the Sunny Island’s output from 120 to
240 volt.

We need to select a generator for backup. We need a two-wire electric start
(in order to be controlled by the Sunny Island) and preferably a generator
that is okay just running 120 volt loads since the Sunny Islands input is
only 120 volt. Something in the 3 kVA -7 kVA range should be fine.

Does anyone have experience or ideas about what kind of two-wire start
generator we might select?

Thanks,

August

Luminalt
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org



 

--

Chris Mason

NABCEP Certified Solar PV Installer™

Solar Design Engineer

Generac Generators Industrial technician

 

264.235.5670

869.662.5670

Skype: netconcepts



_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to