Thank you all for your help. Ray gets the gold star long distance diagnostics 
award as it was simply a thin layer of ice underneath the air cleaner. I 
cleared that out and it started right up and ran in good shape.
Dave

Sent from my iPhone

> On Jan 9, 2018, at 3:35 PM, Chris Mason <cometenergysyst...@gmail.com> wrote:
> 
> If the unit is still under warranty, have any Generac dealer run through
> the diagnostics. The testing flow suggests rotor or stator problems, and
> there is a proscribed testing flow that needs to be performed. If it is
> determined to be a warranty issue, it will be fixed for you at no cost.
> If it is not under warranty, I would still have a dealer look at it. There
> are a large number of possible issues and you are going to spend a lot of
> time trying to find the problem. A Generac tech will likely find the
> problem in a few minutes unless it is a serious problem, in which case you
> were never going to find it.
> I'm a Generac tech so I can speak from some experience that this is likely
> not a simple issue.
> 
>> On Mon, Jan 8, 2018 at 8:13 PM, David Palumbo <palumbo1...@gmail.com> wrote:
>> 
>> I am troubleshooting a 6kw EcoGen LP gas generator in my neighborhood that
>> starts quickly
>> • but immediately shuts down with an “Under Voltage” shutdown alarm
>> • I can clear shutdown alarm and restart with same result. I tried this a
>> few times with same result. One of the start attempts included a back fire
>> before shutting down.
>> • Generator was recently run successfully for a few hours during a cold
>> snap. Started after several attempts at -10 F.
>> • According to the EcoGen manual this Under Voltage alarm is triggered “If
>> the generator voltage falls below 85% of nominal for more than 15
>> seconds”.  This definitely isn’t happening as the generator starts as usual
>> but shuts down within one or two seconds.
>> I will check for fouled spark plugs tomorrow. Anything else that might be
>> the problem?
>> 
>> David Palumbo
>> Independent Power LLC
>> Hyde Park, VT
>> 802-371-8678 voice or text
>> 
>> Sent from Mail for Windows 10
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches@lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
>> org/maillist.html
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
> 
> 
> -- 
> Chris Mason
> NABCEP Certified Solar PV Installer™
> Solar Design Engineer
> Generac Generators Industrial technician
> 
> www.cometsolar.com <http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
_______________________________________________
List sponsored by Redwood Alliance

List Address: RE-wrenches@lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: 
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
www.members.re-wrenches.org

Reply via email to